Burnt bus

Previous Topic: Double-tapped neutrals = massive char-job.. - Topic - Next Topic: 240-volt AFCI breaker New TopicReply to TopicShare Topic
Posted By  
View Profile
Wyckoff, NJ
Posts: 437
Joined: Dec, 2010
Currently offline offline
  
Thread Start First Page
[#1] Posted: 01/03/2011 - 06:17:34 AM
Reply with Quote
Is this a sign of a burnt bus or just discolored metal?

Click to View

56.6 KB

We can't solve problems by using the same kind of thinking we used when we created them
Albert Einstein
View Profile
Swansea, IL
Posts: 1360
Joined: Mar, 2006
Currently offline offline
  
Burnt bus
[#2] Posted: 01/03/2011 - 06:57:29 AM
Reply with Quote
Looks like heat damage to me.

And in unrelated news, I don't see many 150 amp main disconnects.

Mark A. Perry
www.ahis1.com
View Profile
Wyckoff, NJ
Posts: 437
Joined: Dec, 2010
Currently offline offline
  
Burnt bus
[#3] Posted: 01/03/2011 - 07:14:18 AM
Reply with Quote
Cheap builder, minimums only. Thanks.
We can't solve problems by using the same kind of thinking we used when we created them
Albert Einstein
View Profile
Lafayette, Louisiana
Posts: 3918
Joined: Nov, 2009
Currently offline offline
  
Burnt bus
[#4] Posted: 01/03/2011 - 07:18:06 AM
Reply with Quote
Given the limitations of inspecting via a photo, I wouldn't judge this one worthy of mention.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Collins, NY
Posts: 3167
Joined: Apr, 2008
Currently offline offline
  
Burnt bus
[#5] Posted: 01/03/2011 - 09:35:41 AM
Reply with Quote
Quote: Originally posted by Mark P


And in unrelated news, I don't see many 150 amp main disconnects.


My brother put in a 150 amp panel last year, space for lots more circuits (30 max, IIRC) than his 1964 125 amp panel and as an added bonus; now the main, meter and SEC ratings all match.

The panel in the OP is fried.

Tom

http://clearcreekhomeinspection.com/

Life is tough enough as it is, it's tougher when your stupid. Don't do stupid things.
Dr Joe Lstiburek
View Profile
Newberg, OR
Posts: 2787
Joined: Mar, 2007
Currently offline offline
  
Burnt bus
[#6] Posted: 01/03/2011 - 09:48:26 AM
Reply with Quote
I agree with Marc, but as he said, there are limitations to what show up on a pic.

I've heard from electricians that many bars are discolored prior to installation.
Here are some recipes for discoloring copper: http://www.sciencecompany.com/...ulas.htm

Brandon

Portland Home Inspector
View Profile
Victoria, British Columbia
Posts: 2450
Joined: Nov, 2009
Currently offline offline
  
Burnt bus
[#7] Posted: 01/03/2011 - 10:30:49 AM
Reply with Quote
This is a 2826 square foot, single family home built in 1998.

I don't think that would be a copper bus, would it? It is possible with a house that size, that the service is somewhat undersized, which could certainly lead to overheating of the bus. With just the one pic to go on, I'd call for a more thorough check of the panel by an electrician.

Allseason, you should rename your pics before you post them.

www.allsafehome.ca
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Burnt bus
[#8] Posted: 01/03/2011 - 11:39:22 AM
Reply with Quote
Quote: Originally posted by allseason

Is this a sign of a burnt bus or just discolored metal?


There's no way to tell from the picture. It could be completely unimportant discoloration or it could be a loose connection.

This might be one of those times when it's prudent to ask an electrician to pull the main breaker and have a closer look.

- Jim Katen, Oregon

Jim Katen, Oregon
www.amipdx.com
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Burnt bus
[#9] Posted: 01/03/2011 - 11:42:47 AM
Reply with Quote
Quote: Originally posted by John Kogel

This is a 2826 square foot, single family home built in 1998.

I don't think that would be a copper bus, would it?

Sure it could. There are still lots of bare copper buses out there.


Quote: It is possible with a house that size, that the service is somewhat undersized, which could certainly lead to overheating of the bus.

Except that, with a 150-amp main breaker, normal use is unlikely to cause the bus to overheat. That bar can conduct a heck of a lot more power than 150 amps. And if the service were to draw more, I'd expect the main breaker to trip after a while. If the discoloration is caused by overheating, it's probably because the connection is loose.

- Jim Katen, Oregon

Jim Katen, Oregon
www.amipdx.com
View Profile
Victoria, British Columbia
Posts: 2450
Joined: Nov, 2009
Currently offline offline
  
Burnt bus
[#10] Posted: 01/03/2011 - 8:04:37 PM
Reply with Quote
Quote: Originally posted by Jim Katen

Quote: Originally posted by John Kogel

This is a 2826 square foot, single family home built in 1998.

I don't think that would be a copper bus, would it?

Sure it could. There are still lots of bare copper buses out there.


Quote: It is possible with a house that size, that the service is somewhat undersized, which could certainly lead to overheating of the bus.

Except that, with a 150-amp main breaker, normal use is unlikely to cause the bus to overheat. That bar can conduct a heck of a lot more power than 150 amps. And if the service were to draw more, I'd expect the main breaker to trip after a while. If the discoloration is caused by overheating, it's probably because the connection is loose.

- Jim Katen, Oregon
Thanks, Jim. You are right of course. If the breaker is working as it should, there could be tripping but not overheating. And we don't know if the breaker has ever tripped.

I don't see copper, though. In my area, I'd be surprised to see bare copper buses after about 1970.


I mean Copper like in these pics.

Click to View

58.15 KB

Click to View

45.72 KB

Click to View

63.25 KB

www.allsafehome.ca
View Profile
Collins, NY
Posts: 3167
Joined: Apr, 2008
Currently offline offline
  
Burnt bus
[#11] Posted: 01/04/2011 - 04:56:52 AM
Reply with Quote
I've never seen a copper bus panel in person, but wouldn't all the buses be copper? The panel in the OP has aluminum SEC, aluminum lugs, and aluminum straps from the mains to the branch circuit buses. I still think it's smoked.
Tom

http://clearcreekhomeinspection.com/

Life is tough enough as it is, it's tougher when your stupid. Don't do stupid things.
Dr Joe Lstiburek
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Burnt bus
[#12] Posted: 01/04/2011 - 6:44:46 PM
Reply with Quote
Quote: Originally posted by Tom Raymond

I've never seen a copper bus panel in person, but wouldn't all the buses be copper? The panel in the OP has aluminum SEC, aluminum lugs, and aluminum straps from the mains to the branch circuit buses. I still think it's smoked.


Siemens seems to make occasional runs with copper. I see them every so often. We've had people post picture of ITE panels with one copper bus and one aluminum bus on the same panel. Not a problem.

- Jim Katen, Oregon

Jim Katen, Oregon
www.amipdx.com
Chico, CA
Posts: 21
Joined: Dec, 2009
Currently offline offline
  
Burnt bus
[#13] Posted: 01/12/2011 - 8:58:37 PM
Reply with Quote
If the bus in the panel shown in the OP's pic had overheated the plastic behind it would have melted /deformed, it's nothing to worry about in this case.
   
Previous Topic: Double-tapped neutrals = massive char-job.. - Topic - Next Topic: 240-volt AFCI breaker New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.