[#1] Posted: 12/08/2011 - 3:04:14 PM
Reply with Quote
I was in a circa 1890 boarding house recently. Central heat with steam boiler(s), Utica circa 1978. I have not seen a set up like this before, it looks like two boilers with individual burners attached to each other as you would sections of a radiator. When tested only one side fired up. Is the other side to provide addtional heat should the one burner be inadequate or should both run together. There is only one thermostat, TPRV, low water cut off , etc. New to me, anyone familiar with this arrangment?

Click to View

96.2 KB

Click to View

46.66 KB

We can't solve problems by using the same kind of thinking we used when we created them
Albert Einstein
View Profile
State: PA & NJ
Posts: 3232
Joined: Jan, 2004
Currently offline offline
  
Tandem boilers
[#2] Posted: 12/08/2011 - 3:36:03 PM
Reply with Quote
That set-up is common for replacements of big old boilers (easier to get two sections down the narrow basement stairs).

For steam, both sides should be firing.

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
View Profile
Chicago, IL
Posts: 9553
Joined: Dec, 2003
Currently offline offline
  
Tandem boilers
[#3] Posted: 12/08/2011 - 3:38:25 PM
Reply with Quote
What Kibble said.

I see this occasionally, although I've never seen one where only one unit fires.

If there's a single T-stat, it should fire both boilers, no?


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
Rochester, New York
Posts: 4131
Joined: Dec, 2003
Currently offline offline
  
Tandem boilers
[#4] Posted: 12/08/2011 - 5:56:38 PM
Reply with Quote
Quote:
If there's a single T-stat, it should fire both boilers, no?


Like Bill said- for steam both units should fire.

For hydronic, they could be set-up with a pair of aquastats so the second one fires only when the primary cannot keep up with demand ...or they could be setup with one aquastat so that they both fired on demand.

Chad Fabry
StructureSmart Home Inspection Rochester, NY
www.structuresmart.com
View Profile
Chicago, IL
Posts: 9553
Joined: Dec, 2003
Currently offline offline
  
Tandem boilers
[#5] Posted: 12/08/2011 - 6:27:54 PM
Reply with Quote
Yeah, OK. I've just seen them with a single aqua stat, single t-stat, boilers run in parallel.


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
Needham, Massachusetts
Posts: 1845
Joined: Sep, 2003
Currently offline offline
  
Tandem boilers
[#6] Posted: 12/09/2011 - 07:26:14 AM
Reply with Quote
Also, copper risers? That is an unfailing sign of an installer who doesn't understand steam systems.

View Profile
Wyckoff, NJ
Posts: 437
Joined: Dec, 2010
Currently offline offline
  
Tandem boilers
[#7] Posted: 12/09/2011 - 07:50:05 AM
Reply with Quote
Quote: Originally posted by Jim Morrison

Also, copper risers? That is an unfailing sign of an installer who doesn't understand steam systems.


True, but common unfortunately. Thanks for all the input fellas.

We can't solve problems by using the same kind of thinking we used when we created them
Albert Einstein
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#8] Posted: 12/10/2011 - 3:14:31 PM
Reply with Quote
Quote: Originally posted by Jim Morrison

Also, copper risers? That is an unfailing sign of an installer who doesn't understand steam systems.

K-copper?

View Profile
State: PA & NJ
Posts: 3232
Joined: Jan, 2004
Currently offline offline
  
Tandem boilers
[#9] Posted: 12/10/2011 - 5:36:44 PM
Reply with Quote
Quote: Originally posted by plummen

Quote: Originally posted by Jim Morrison

Also, copper risers? That is an unfailing sign of an installer who doesn't understand steam systems.

K-copper?
It doesn't matter what type of copper. It expands and contracts and the joints fail.

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#10] Posted: 12/10/2011 - 6:14:32 PM
Reply with Quote
Are you familiar with brazed type -k copper?
View Profile
State: PA & NJ
Posts: 3232
Joined: Jan, 2004
Currently offline offline
  
Tandem boilers
[#11] Posted: 12/10/2011 - 8:38:37 PM
Reply with Quote
Yes, I am. Are you attempting to defend using copper for steam risers?
Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#12] Posted: 12/11/2011 - 10:47:12 AM
Reply with Quote
Im just saying that sometimes there is more than one option,especially on a small boiler .
My first question on that particular boiler from what i see in the picture is where is the insulation on the lines,and since im willing to bet it was asbestos who removed and how did they remove it.

View Profile
Chicago, IL
Posts: 9553
Joined: Dec, 2003
Currently offline offline
  
Tandem boilers
[#13] Posted: 12/11/2011 - 12:03:12 PM
Reply with Quote

No option on steam. Iron. Pipefitting.


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#14] Posted: 12/11/2011 - 12:44:15 PM
Reply with Quote
http://www.copper.org/applicat...ems.html
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#15] Posted: 12/11/2011 - 12:48:23 PM
Reply with Quote
www.indpipe.com%2Fimages%2FPDF...3tLAz1Q' target='_blank'>http://www.google.com/url?sa=t...u3tLAz1Q
View Profile
Chicago, IL
Posts: 9553
Joined: Dec, 2003
Currently offline offline
  
Tandem boilers
[#16] Posted: 12/11/2011 - 1:25:03 PM
Reply with Quote

Who'd have ever imagined that Copper.org would think it's OK?

Of course there's lots of stuff one can do if they're so inclined.

Personally, I pay attention to the guys installing and working on steam systems for the last century. Other's can listen to professional organization webmeisters.


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
Needham, Massachusetts
Posts: 1845
Joined: Sep, 2003
Currently offline offline
  
Tandem boilers
[#17] Posted: 12/11/2011 - 2:24:57 PM
Reply with Quote
Not only do the joints leak, but the rest of the copper gets perforated. I don't know what flies in other parts of the country, but we rarely see copper risers on a steam system, and when we do, it's obvious why it's such a bad idea. Type K brazed copper? Never seen it on a steam system.
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#18] Posted: 12/11/2011 - 2:43:26 PM
Reply with Quote
Quote: Originally posted by kurt


Who'd have ever imagined that Copper.org would think it's OK?

Of course there's lots of stuff one can do if they're so inclined.

Personally, I pay attention to the guys installing and working on steam systems for the last century. Other's can listen to professional organization webmeisters.


Did you notice the copper guys posted the standards from the engineering books?
You guys seem to like to have it both ways around here.
When it fits what you want its because the national electric code says and thats the only answer,it doesnt matter what problems the guys in the field have with it because they obviously were installing it wrong.
But when the code says it can be done and they show you the standards to back it up it doesnt matter,because the guys in the fitters union dont like to do it that way.
So exactly how many of you guys have a 3rd grade engineers license,or any kind of a back ground or actual hands on experiance other than pointing at a boiler in house?

View Profile
Chicago, IL
Posts: 9553
Joined: Dec, 2003
Currently offline offline
  
Tandem boilers
[#19] Posted: 12/11/2011 - 3:04:19 PM
Reply with Quote
Like I said, there's lots of ways to do stuff. I'm all for engineers saying it's OK and doing it any way they want on their jobs.

The engineers I work with know that copper is a bad way to go.

Everyone gets to choose. I choose what I know works.

Are there a lot of steam systems in Louisville, Nebraska?


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#20] Posted: 12/11/2011 - 3:29:51 PM
Reply with Quote
Ive got an old 93hp kewanee in one of my buildings in omaha,no copper on that one but its also the size of my old chevy cube van and heats 27 apartments and 6 commercial bays.
There are many updated steam boilers around omaha,and many of them have k copper plumbed into them theyve been running for years without issues.
Many of the hot water boilers I still work on around omaha still run steel piping,some of them have been repiped in copper it depends on when they were installed.

View Profile
Ridgewood, NJ
Posts: 952
Joined: Sep, 2002
Currently offline offline
  
Tandem boilers
[#21] Posted: 12/11/2011 - 5:26:41 PM
Reply with Quote
Quote: Originally posted by Jim Morrison

Also, copper risers? That is an unfailing sign of an installer who doesn't understand steam systems.
Copper risers for the Peerless steam boiler my basement. 23 years old and no leakage whatsover.

And yup, it's piped with a bullheaded tee...

Any chance there was an outdoor reset for that system?

Neal Lewis
www.totalhomeinspectionservices.com
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#22] Posted: 12/11/2011 - 7:58:49 PM
Reply with Quote
So is there anything in a mechanical code book that says you can never use K-copper under any circumstances in any steam boiler?
I mean since most of you guys(not all of you)seem to like to get your answers directly from a book.

View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#23] Posted: 12/11/2011 - 8:00:29 PM
Reply with Quote
Quote: Originally posted by Neal Lewis

Quote: Originally posted by Jim Morrison

Also, copper risers? That is an unfailing sign of an installer who doesn't understand steam systems.
Copper risers for the Peerless steam boiler my basement. 23 years old and no leakage whatsover.

And yup, it's piped with a bullheaded tee...

Any chance there was an outdoor reset for that system?
Could you post a picture of your boiler install?

View Profile
Chicago, IL
Posts: 9553
Joined: Dec, 2003
Currently offline offline
  
Tandem boilers
[#24] Posted: 12/11/2011 - 8:07:53 PM
Reply with Quote

Oh, lighten up.

You show up out of nowhere and proceed to respond to every post from the last 5 years, then go all agro with a bunch of strangers.

Use copper of it's important to you.

Sheesh.......


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
Tandem boilers
[#25] Posted: 12/11/2011 - 8:35:13 PM
Reply with Quote
No you need to lighten up ,i went through the same bunch of crap from you guys on the A coil post when i talked about using oversize coils with you guys rattling on about i didnt know what i was talking about,then i posted the manufacturers suggestions for over size coils proving it was legitimate.
As i was basically told years of field experiance meant nothing if it wasnt designed by an engineer or in a code book .
So now im just asking where it says in the code that K-copper cannot never be used in a steam boiler system,and no the experiance from old guys whove been in the field for 100 years doesnt count as you guys have already said.

View Profile
State: PA & NJ
Posts: 3232
Joined: Jan, 2004
Currently offline offline
  
Tandem boilers
[#26] Posted: 12/11/2011 - 9:30:44 PM
Reply with Quote
Plummen,

Go over here with your babbling: http://www.heatinghelp.com/for...ly-Steam

Be sure to post your opinion about using copper for near-boiler piping for steam boilers. I'm sure they'll all be in awe of your knowledge.

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
 
 1  2 - Next 
Previous Topic: todays finds - Topic - Next Topic: A coil/Condensor sizing New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000