[#1] Posted: 03/26/2012 - 11:23:40 PM
Reply with Quote
My understanding is that the grounding electrode conductors should be connected on the same bus which the grounded service conductor (service neutral) is connected to. The GEC's in this panel are terminated on this panel's 2-bonded equipment ground bars.

(one GEC is clamped to the copper municipal supply line, and the other to a driven rod)

I just want to make certain that I am correct in calling this out, and of course to have this discussed here so that others can benefit.

Click to View

69.63?KB

Dave Tontarski
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
GEC's On EGC Bars - Not Service Neutral Bar
[#2] Posted: 03/27/2012 - 12:07:37 AM
Reply with Quote
I believe that the applicable article is 250.24(A)(4). As I read it, you're not supposed to rely on the screw as a bonding jumper in this case. You'd need a properly sized wire between the neutral terminal bar and the equipment grounding bar.

Alternatively, you could run the GEC right to the neutral bar with an appropriate accessory lug.


Jim Katen, Oregon
www.amipdx.com
View Profile
Rochester, New York
Posts: 275
Joined: Feb, 2006
Currently offline offline
  
GEC's On EGC Bars - Not Service Neutral Bar
[#3] Posted: 03/27/2012 - 12:11:09 AM
Reply with Quote
Thanks Jim.

Would it suffice to have just one of these GEC's connected to the neutral terminal bar on an appropriate lug (one is present) or with an appropriate sized wire, or would both of these be required to be terminated on this bar?

Dave Tontarski
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
GEC's On EGC Bars - Not Service Neutral Bar
[#4] Posted: 03/27/2012 - 10:35:54 AM
Reply with Quote
Quote: Originally posted by dtontarski

Thanks Jim.

Would it suffice to have just one of these GEC's connected to the neutral terminal bar on an appropriate lug (one is present) or with an appropriate sized wire, or would both of these be required to be terminated on this bar?


If they go to different parts of the grounding electrode system - for instance one goes to a set of driven rods and the other goes to a water supply pipe - then they should both be connected to the neutral conductor with a terminal bar or a wire - not a screw.

Jim Katen, Oregon
www.amipdx.com
LaPorte, IN
Posts: 14
Joined: Apr, 2012
Currently offline offline
  
GEC's On EGC Bars - Not Service Neutral Bar
[#5] Posted: 04/16/2012 - 11:21:07 AM
Reply with Quote
The GECs should have been terminated next to the grounded service conductor at the top center of the load center. Lug screws are provided there.
   
Previous Topic: Overfull panel - Topic - Next Topic: Fried main breaker and SEC - Crappy repair? New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000