[#1] Posted: 04/09/2012 - 4:11:57 PM
Reply with Quote
I've a contract to replace a 200A FPE load center but it has to be installed 4' further down the wall to get adequate access.

I'm just being cautious because I can't recall ever running 2/0 2 conductor SE cable inside a wall without conduit. Couldn't find anything against it in the 2008 NEC.

Anyone aware of a prohibition, before I spend all that dough? There's no way I could possibly fit conduit into this space.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Type SE cable in walls
[#2] Posted: 04/09/2012 - 7:43:32 PM
Reply with Quote
Quote: Originally posted by Marc

I've a contract to replace a 200A FPE load center but it has to be installed 4' further down the wall to get adequate access.

I'm just being cautious because I can't recall ever running 2/0 2 conductor SE cable inside a wall without conduit. Couldn't find anything against it in the 2008 NEC.

Anyone aware of a prohibition, before I spend all that dough? There's no way I could possibly fit conduit into this space.

Marc


It's fine. Just provide protection and secure it per the usual requirements.


Jim Katen, Oregon
www.amipdx.com
Chestertown, MD
Posts: 214
Joined: Apr, 2009
Currently offline offline
  
Type SE cable in walls
[#3] Posted: 04/09/2012 - 8:42:39 PM
Reply with Quote
Is this going to create an issue with the overcurrent protection distance inside the house?
View Profile
Lafayette, Louisiana
Posts: 3918
Joined: Nov, 2009
Currently offline offline
  
Type SE cable in walls
[#4] Posted: 04/10/2012 - 08:08:41 AM
Reply with Quote
As I recall, the local AHJ's don't like to see more than 6' of distance between the meter box and the SE main disconnecting means. Actual distance on this job is more like 4 or 5'. I'm buying 6' of SE but I expect to trim it during the installation

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Comer, GA
Posts: 1019
Joined: Apr, 2004
Currently offline offline
  
Type SE cable in walls
[#5] Posted: 04/11/2012 - 06:58:10 AM
Reply with Quote
I recall a session by an IAEI troup of engineers where an electrician tried to pin them down on that distance. They squirmed in their seats and would not give a figure.
"Emancipate yourself from mental slavery, for only ourselves can free our minds"-Bob Marley
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Type SE cable in walls
[#6] Posted: 04/11/2012 - 08:52:03 AM
Reply with Quote
Quote: Originally posted by Jim Baird

I recall a session by an IAEI troup of engineers where an electrician tried to pin them down on that distance. They squirmed in their seats and would not give a figure.


That's because there isn't a figure and a question that asks for one lacks foundation.

Here's the applicable phrase from 225.32:
The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors.

An AHJ might *make up* a more concrete requirement, but it would be just that, a made up requirement. The actual code language provides a concept, not a concrete distance.

Jim Katen, Oregon
www.amipdx.com
View Profile
Collins, NY
Posts: 3167
Joined: Apr, 2008
Currently offline offline
  
Type SE cable in walls
[#7] Posted: 04/11/2012 - 09:01:34 AM
Reply with Quote
There must have been suggestive language somewhere. It's too big a coincidence that the customary number to *make up* is 6'.
Tom

http://clearcreekhomeinspection.com/

Life is tough enough as it is, it's tougher when your stupid. Don't do stupid things.
Dr Joe Lstiburek
View Profile
Lafayette, Louisiana
Posts: 3918
Joined: Nov, 2009
Currently offline offline
  
Type SE cable in walls
[#8] Posted: 04/11/2012 - 10:02:24 AM
Reply with Quote
Quote: Originally posted by Tom Raymond

There must have been suggestive language somewhere. It's too big a coincidence that the customary number to *make up* is 6'.


It's like the SOP. One state dreams one up and the rest just watch and follow like chickens. Ever seen chickens in a coop?

But...there's a few, uhhh, regulatory bodies out there that did indeed put their thinking cap on and did some thinking about it. Absolutely, and a few did manage to do a swell job of it.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Type SE cable in walls
[#9] Posted: 04/11/2012 - 2:26:13 PM
Reply with Quote
Quote: Originally posted by Tom Raymond

There must have been suggestive language somewhere. It's too big a coincidence that the customary number to *make up* is 6'.


First, as far as I can tell there is no "customary" distance. Everywhere seems to be slightly different. In Oregon, for instance, you're allowed a horizontal distance equal to one stud bay.

I just traced the requirement back through the ages to the 1947 edition and, while the requirement jumps around a bit, the actual wording is very consistent. It never specifies a specific distance, just, "nearest to the entrance of the conductors."

Jim Katen, Oregon
www.amipdx.com
   
Previous Topic: Fan rated for shower installation - Topic - Next Topic: type CP breaker for A/C unit New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000