[#1] Posted: 04/11/2012 - 07:38:14 AM
Reply with Quote
I have a house with flex duct that was placed in 2001. Our town inspector is telling me that ICC code stipulates that this duct work be replaced with metal duct or encased/boxed in. I can't find any ICC code to support this. Can anyone confirm material requirements for duct work?



View Profile
Gaston, Oregon
Posts: 8083
Joined: Dec, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#2] Posted: 04/11/2012 - 08:40:33 AM
Reply with Quote
Quote: Originally posted by MRB

I have a house with flex duct that was placed in 2001. Our town inspector is telling me that ICC code stipulates that this duct work be replaced with metal duct or encased/boxed in. I can't find any ICC code to support this. Can anyone confirm material requirements for duct work?




He should provide you with the citation to back up his claim.

Jim Katen, Oregon
www.amipdx.com
View Profile
Collins, NY
Posts: 3142
Joined: Apr, 2008
Currently offline offline
  
Duct Material Requirements per ICC
[#3] Posted: 04/11/2012 - 08:54:33 AM
Reply with Quote
I can't imagine a scenario where an AHJ would have anything to say about 11 year old ducts.
Tom

http://clearcreekhomeinspection.com/

Life is tough enough as it is, it's tougher when your stupid. Don't do stupid things.
Dr Joe Lstiburek
View Profile
Rochester, New York
Posts: 4114
Joined: Dec, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#4] Posted: 04/11/2012 - 10:00:53 AM
Reply with Quote
Quote: Originally posted by Tom Raymond

I can't imagine a scenario where an AHJ would have anything to say about 11 year old ducts.


Really? I've seen AHJ's that have something to say about picnic tables stored in barns. (accused the owner of using the barn as a vacation home)

There are a ton of AHJ's that have never built anything, and who couldn't fix a sandwich.

It's a game the State plays called "pin the badge on the donkey"

They give an ass a badge then sit back and watch the ego take over.

Chad Fabry
StructureSmart Home Inspection Rochester, NY
www.structuresmart.com
View Profile
Collins, NY
Posts: 3142
Joined: Apr, 2008
Currently offline offline
  
Duct Material Requirements per ICC
[#5] Posted: 04/11/2012 - 10:13:12 AM
Reply with Quote
Ok, your right. I should have said 'has authority over'.

I'd ask them to PFO.

Tom

http://clearcreekhomeinspection.com/

Life is tough enough as it is, it's tougher when your stupid. Don't do stupid things.
Dr Joe Lstiburek
Glen Ridge, NJ
Posts: 7
Joined: Apr, 2012
Currently offline offline
  
Duct Material Requirements per ICC
[#6] Posted: 04/11/2012 - 10:49:37 AM
Reply with Quote
He's now referenced two codes which have no relevance to duct material. One referenced fire blocking requirements and the second referenced requirements for duct connectors. I've had three professional sources tell me my duct material is sufficient and I want to offer up a few more so that we can move on and close on our house in a timely manner.
View Profile
Kenmore, WA
Posts: 15390
Joined: Dec, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#7] Posted: 04/11/2012 - 12:31:58 PM
Reply with Quote
Where/how is the duct being used?

Are you talking about an exhaust vent or an actual heating duct?

Exactly what is connected to either end of the duct?

What type of "connector" is the source he's cited referring to?

Does it pass through a floor, ceiling or wall plane?

Photographs?

What are the two codes that he's citing?

Have you talked with his/her supervisor?

ONE TEAM - ONE FIGHT!!!

Mike

View Profile
Chicago, IL
Posts: 9505
Joined: Dec, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#8] Posted: 04/11/2012 - 1:10:12 PM
Reply with Quote
All the things everyone else said. Without more specific details, it's hard to imagine what the guy is talking about.


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
Gaston, Oregon
Posts: 8083
Joined: Dec, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#9] Posted: 04/11/2012 - 2:30:56 PM
Reply with Quote
Quote: Originally posted by MRB

He's now referenced two codes which have no relevance to duct material. One referenced fire blocking requirements and the second referenced requirements for duct connectors. I've had three professional sources tell me my duct material is sufficient and I want to offer up a few more so that we can move on and close on our house in a timely manner.


I don't know how he's trying to apply the fire blocking rules. Do the flex ducts penetrate a garage wall or some other area that requires blocking?

The duct connector citation is an easy one to mis-apply. It shows up on the home inspector discussion boards regularly. People often don't realize that flex ducts and flex duct connectors are two different things. Flex duct connectors have a limitation on length.

This sounds like you're talking about a home inspector, not a town inspector. Is that right? If it's really the town inspector, why does he have any say in a real estate transaction?

Jim Katen, Oregon
www.amipdx.com
Glen Ridge, NJ
Posts: 7
Joined: Apr, 2012
Currently offline offline
  
Duct Material Requirements per ICC
[#10] Posted: 04/11/2012 - 2:48:57 PM
Reply with Quote
This is all coming from our town inspector. I have spoken to the town administrator but he cannot try to influence the inspector with regard to enforcement but has helped me expedite the matter.

It really comes down to the material used which the inspector says must be replaced entirely through out the entire system. He is basically saying if we have flexible duct it must be enclosed and the other option is to change out with metal. In his opinion flex duct is not sufficient on its own.

Here's a photo of the ductwork.

Click to View

44.32 KB

The one code I found regarding duct materials is M1601.1.1. Our material would be class 1.

View Profile
Rochester, New York
Posts: 4114
Joined: Dec, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#11] Posted: 04/11/2012 - 3:10:45 PM
Reply with Quote
Did the home lose its C/O for some reason? Why is the AHJ inside the home?
Chad Fabry
StructureSmart Home Inspection Rochester, NY
www.structuresmart.com
Glen Ridge, NJ
Posts: 7
Joined: Apr, 2012
Currently offline offline
  
Duct Material Requirements per ICC
[#12] Posted: 04/11/2012 - 3:13:48 PM
Reply with Quote
Quote: Originally posted by Chad Fabry

Did the home lose its C/O for some reason? Why is the AHJ inside the home?


Our town requires a new C/O when there is an ownership change.

View Profile
Oak Park, IL
Posts: 122
Joined: Mar, 2011
Currently offline offline
  
Duct Material Requirements per ICC
[#13] Posted: 04/11/2012 - 4:13:10 PM
Reply with Quote
Quote: Originally posted by MRB

Our town requires a new C/O when there is an ownership change.


There are several cities around here that require an inspection from a city guy prior to a real estate transaction. But I don't think they ever go in the attic, and ductwork is definitely way beyond their interest level. Mostly they're looking for smoke/CO alarms, GFCI, grounded receptacles, hose spigots with anti-siphon, etc.

MRB, I wish you luck. I think the guy you're dealing with is off his nut.

Steve Nations
NationsHomeInspections.com
View Profile
State: PA & NJ
Posts: 3208
Joined: Jan, 2004
Currently offline offline
  
Duct Material Requirements per ICC
[#14] Posted: 04/11/2012 - 5:34:49 PM
Reply with Quote
If the home previously passed all final construction inspections, then a resale C/O should only include:
Smoke detector on each level and bedrooms, C/O detectors 10' from each bedroom and a fire extinguisher w/in 10' of the kitchen.

He's overreaching. Up in that corner of the state, it could be that he's fi$hing. Get a hidden camera

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
Glen Ridge, NJ
Posts: 7
Joined: Apr, 2012
Currently offline offline
  
Duct Material Requirements per ICC
[#15] Posted: 04/11/2012 - 5:50:20 PM
Reply with Quote
Quote: Originally posted by Bill Kibbel

If the home previously passed all final construction inspections, then a resale C/O should only include:
Smoke detector on each level and bedrooms, C/O detectors 10' from each bedroom and a fire extinguisher w/in 10' of the kitchen.

He's overreaching. Up in that corner of the state, it could be that he's fi$hing. Get a hidden camera


Bill is there any code which states he should only be looking for those items? I'd like to state in my response.

View Profile
Chicago, IL
Posts: 9505
Joined: Dec, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#16] Posted: 04/11/2012 - 5:52:04 PM
Reply with Quote
The pic doesn't show up....change the name to all letters, no spaces.

Yes, I agree. You're dealing with a nut job who's making broad interpretations on something I don't think he really knows much about.


Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


View Profile
Marin County, CA
Posts: 342
Joined: Mar, 2002
Currently offline offline
  
Duct Material Requirements per ICC
[#17] Posted: 04/11/2012 - 8:28:23 PM
Reply with Quote
You can go here

http://bulk.resource.org/codes...tial.pdf

and download a copy of the New Jersey residential code. You will see in the beginning pages of it that no amendments were made to IRC chapter 16, and that the sections you cited do indeed permit class 0 and class 1 ducts. I suggest photographing the "class 1" label and printing out the pages on ducts (chapter 16 is only 4 pages long) and writing a letter stating your case. The city is supposed to have an appeals board for these issues. If they don't, then I would submit it to the city attorney and the town council.

If the ducts were class 2 (something that hasn't been placed in houses for over 20 years now) the inspector could legitimately ask to have them replaced. If the ducts were inside an attached garage, he could ask to have that portion within the garage replaced. If there is some other documentable specific failure to comply with the rules in chapter 16, then a correction notice could be issued forcing you to comply with those written rules. It doesn't sound like any of that is the problem, and the real problem is likely to be the one that Bill suspects.

You will be doing a favor to your fellow citizens by not knuckling under. Something needs to be brought into compliance in your town, and it isn't your duct system.




Douglas Hansen
www.codecheck.com
View Profile
State: PA & NJ
Posts: 3208
Joined: Jan, 2004
Currently offline offline
  
Duct Material Requirements per ICC
[#18] Posted: 04/11/2012 - 9:14:11 PM
Reply with Quote
Quote: Originally posted by MRB

Quote: Originally posted by Bill Kibbel

If the home previously passed all final construction inspections, then a resale C/O should only include:
Smoke detector on each level and bedrooms, C/O detectors 10' from each bedroom and a fire extinguisher w/in 10' of the kitchen.

He's overreaching. Up in that corner of the state, it could be that he's fi$hing. Get a hidden camera


Bill is there any code which states he should only be looking for those items? I'd like to state in my response.
What I stated is typical for several NJ municipalities for issuing a "continued use" C/O. It's not a statewide code.

Could there possibly be a previous permit on the structure that never closed with a final inspection? I think it can only be one of the two issues I mentioned that would cause the building official to not allow continued occupancy of the building.

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
View Profile
Ridgewood, NJ
Posts: 949
Joined: Sep, 2002
Currently offline offline
  
Duct Material Requirements per ICC
[#19] Posted: 04/11/2012 - 9:56:18 PM
Reply with Quote
Quote: Originally posted by Bill Kibbel

If the home previously passed all final construction inspections, then a resale C/O should only include:
Smoke detector on each level and bedrooms, C/O detectors 10' from each bedroom and a fire extinguisher w/in 10' of the kitchen.
Bill, every town I deal with checks these items as a minimum. I thought it was a statewide code, but i don't check them anyway. The building dept or fire dept inspects them and issues the certification. Above that, the town can check for whatever they want, without rhyme or reason. It's almost impossible to keep track of what each town is checking for with the C/O inspections.

Neal Lewis
www.totalhomeinspectionservices.com
View Profile
Succasunna, NJ
Posts: 1024
Joined: Sep, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#20] Posted: 04/12/2012 - 03:18:45 AM
Reply with Quote
Different towns have different CCO requirements. Morris Township & Summit are 2 that I know of that conduct more stringent inspections.

Who is doing your inspection; is it a 'building code inspector' or is it a 'code inspector'. I know of one town who hired the retired chief of police to conduct 'code inspections'.

If it's the building code inspector, your options are to go the the construction official and talk to him/her OR call the DCA 609- 984-7609. Tell them your situation and they should be able to lead you in the right direction.

(by the way, the former chief of police "failed" a CCO inspection because of failing steel posts in a basement; he then proceeded to hand the RE a contractors card who just happened to be his son) The town shall remain nameless.


Darren
Succasunna NJ

New Jersey Home Inspections

"Leave my nose alone Please!" (FZ)
View Profile
Succasunna, NJ
Posts: 1024
Joined: Sep, 2003
Currently offline offline
  
Duct Material Requirements per ICC
[#21] Posted: 04/12/2012 - 03:21:13 AM
Reply with Quote


Download Attachment: Ducts.pdf
15.22 KB

Darren
Succasunna NJ

New Jersey Home Inspections

"Leave my nose alone Please!" (FZ)
View Profile
Lafayette, Louisiana
Posts: 3850
Joined: Nov, 2009
Currently online online
  
Duct Material Requirements per ICC
[#22] Posted: 04/12/2012 - 06:47:22 AM
Reply with Quote
I had to google flexible air connector to learn what that term meant.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
Glen Ridge, NJ
Posts: 7
Joined: Apr, 2012
Currently offline offline
  
Duct Material Requirements per ICC
[#23] Posted: 04/12/2012 - 08:20:12 AM
Reply with Quote
Thanks for posting Marc. I found something similar and sent to the inspector. He's not replied to any of my emails and just returned two phone calls. I suspect he doesn't want to put anything in writing.
I have the owners of two separate HVAC companies trying to contact him to get to the bottom of this as well.

Quote: Originally posted by Marc

I had to google flexible air connector to learn what that term meant.

Marc

Glen Ridge, NJ
Posts: 7
Joined: Apr, 2012
Currently offline offline
  
Duct Material Requirements per ICC
[#24] Posted: 04/12/2012 - 08:23:27 AM
Reply with Quote
Thanks for the input Douglas. I took your advice and sent him a photo of the ductwork showing Class 1 printed on the side. I had also sent him a link to the Chapter 16 section on ducts. I have yet to speak with anyone who can support any notion that our ducts need to be replaced or enclosed. Hoping to wrap up today.

Quote: Originally posted by Douglas Hansen

You can go here

http://bulk.resource.org/codes...tial.pdf

and download a copy of the New Jersey residential code. You will see in the beginning pages of it that no amendments were made to IRC chapter 16, and that the sections you cited do indeed permit class 0 and class 1 ducts. I suggest photographing the "class 1" label and printing out the pages on ducts (chapter 16 is only 4 pages long) and writing a letter stating your case. The city is supposed to have an appeals board for these issues. If they don't, then I would submit it to the city attorney and the town council.

If the ducts were class 2 (something that hasn't been placed in houses for over 20 years now) the inspector could legitimately ask to have them replaced. If the ducts were inside an attached garage, he could ask to have that portion within the garage replaced. If there is some other documentable specific failure to comply with the rules in chapter 16, then a correction notice could be issued forcing you to comply with those written rules. It doesn't sound like any of that is the problem, and the real problem is likely to be the one that Bill suspects.

You will be doing a favor to your fellow citizens by not knuckling under. Something needs to be brought into compliance in your town, and it isn't your duct system.





   
Previous Topic: Heat pump/oil burner combo - Topic - Next Topic: Floor Heater Clearance New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000