Grounding of equipment and bonding of all permanent installed metallic items in and around pools is always a concern of mine. What do you think and say about metal downspout within 4' and metal guttering/roof drip edge within 8'6" as depicted?

Download Attachment: Metalgutterpool.JPG
94.93 KB

Barry Adair
trec#4563
http://www.adairinspection.com
life is the random lottery of events followed by numerous narrow escapes...accept the good
Indian Rocks Beach, Florida
Posts: 152
Joined: Feb, 2004
Currently offline offline
  
to bond or not?
[#2] Posted: 05/21/2006 - 4:25:34 PM
Reply with Quote
Quote:Originally posted by BADAIR

Grounding of equipment and bonding of all permanent installed metallic items in and around pools is always a concern of mine. What do you think and say about metal downspout within 4' and metal guttering/roof drip edge within 8'6" as depicted?

Download Attachment: Metalgutterpool.JPG
94.93 KB


The downspout requires bonding.

Mark Cramer
http://www.BestTampaInspector.com
View Profile
Harrisonburg, Virginia
Posts: 116
Joined: Dec, 2006
Currently offline offline
  
to bond or not?
[#3] Posted: 02/17/2007 - 10:15:23 AM
Reply with Quote
(5) Metal Wiring Methods and Equipment. Metalsheathed
cables and raceways, metal piping, and all fixed
metal parts except those separated from the pool by a permanent
barrier shall be bonded that are within the following
distances of the pool:
(1) Within 1.5 m (5 ft) horizontally of the inside walls of
the pool

(2) Within 3.7 m (12 ft) measured vertically above the
maximum water level of the pool, or any observation
stands, towers, or platforms, or any diving structures

Yep, in this picture it should be bonded.

Paul Abernathy,CME,CEPE
National Electrical Code Expert & Training Consultant
VA State Certified Master Electrician- 20+ Years Experience
ICC® & IAEI® Certified Electrical Inspector
NFPA 70E Safety Consultant
Web: www.TheElectricalGuru.com

Check me out in Mike Holts 2008 NEC Exam Prep Series.
   
Previous Topic: Free NEC Pool Interpretation From Mike Holt - Topic - Next Topic: Installment 4 New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000