to bond or not?
[#2] Posted: 05/21/2006 - 4:25:34 PM |  | |
|
Quote: Originally posted by BADAIRGrounding of equipment and bonding of all permanent installed metallic items in and around pools is always a concern of mine. What do you think and say about metal downspout within 4' and metal guttering/roof drip edge within 8'6" as depicted? Download Attachment: Metalgutterpool.JPG94.93 KB
The downspout requires bonding.
|
Mark Cramer http://www.BestTampaInspector.com |
| |
|
|
| |
 |
Harrisonburg, Virginia Posts: 116
Joined: Dec, 2006
| offline |
|
to bond or not?
[#3] Posted: 02/17/2007 - 10:15:23 AM |  | |
|
(5) Metal Wiring Methods and Equipment. Metalsheathed cables and raceways, metal piping, and all fixed metal parts except those separated from the pool by a permanent barrier shall be bonded that are within the following distances of the pool: (1) Within 1.5 m (5 ft) horizontally of the inside walls of the pool (2) Within 3.7 m (12 ft) measured vertically above the maximum water level of the pool, or any observation stands, towers, or platforms, or any diving structures
Yep, in this picture it should be bonded.
|