 Voltage drops reading on the suretest
Errors and Omissions Insurance for home inspectors, appraisers, agents, brokers and other real estate professionals.   
Previous Topic: Bought Another Fenix - Topic - Next Topic: Fluke 62 New TopicReply to TopicShare Topic Printer FriendlyBookmark this Topic
Posted By  
Starting Member
West Jordan, Utah
Posts: 1
Joined: Feb, 2010
Currently offline offline
  
Thread Start First Page
[#1] Posted: Feb 01 2010 - 6:12:55 PM
Reply with Quote
I get voltage drop readings on the suretest over 5% all the time but when I check the volts from the panel and at the outlet I see 120 aprx. should I ignore the voltage drop reading?

God bless us one and all!
View Profile
Editor - TIJ

Kenmore, WA
Posts: 12154
Joined: Dec, 2003
Currently online online
  
Voltage drops reading on the suretest
[#2] Posted: Feb 01 2010 - 6:21:03 PM
Reply with Quote
The acceptable range for voltage is 108 to 132 volts. They used to say that a 10% drop was unacceptable. 108 is a 12 volt drop from 120 volts or 10%, no? I guess that's where they came up with the 108 volts.

Anyway, I've mellowed over the years. I think I'd only report it if it was in excess of 10% and reading less than 108 volts. I don't think you're going to see that with new wiring but you might see it with K & T or some of the older post-WWII stuff.

ONE TEAM - ONE FIGHT!!!

Mike

View Profile
Senior Member

Spring Hill (Nashville area), Tennessee
Posts: 2581
Joined: Nov, 2003
Currently offline offline
  
Voltage drops reading on the suretest
[#3] Posted: Feb 02 2010 - 06:50:15 AM
Reply with Quote
That is one of the problems (not really a problem, but just too much information) with a ShureTest tester. I use to report voltage drops, but I got so tired of electricians saying that they could not really do anyting about it because it was an issue with the utility company. Then everyone would look at me for an answer.

I stopped looking voltage drops many years back.

Scott Patterson
http://www.traceinspections.com

"Minds are like parachutes they only function when open"
View Profile
Associate Editor - TIJ

Charlestown, Massachusetts
Posts: 1399
Joined: Sep, 2003
Currently offline offline
  
Voltage drops reading on the suretest
[#4] Posted: Feb 02 2010 - 07:37:14 AM
Reply with Quote
You should do a search of these forums for that info, because it has been discussed at length in the past. Jim Katen had a nice treatise on the subject as I recall.
Jim
www.AlMorrison.com
www.CasasDelMarPV.com
View Profile
Active Member

Louisville, KY
Posts: 466
Joined: Jan, 2010
Currently offline offline
  
Voltage drops reading on the suretest
[#5] Posted: Feb 04 2010 - 09:59:48 AM
Reply with Quote
I had a bathroom the other day with 12.8vd @20amp. The house had many other eletrical issues as well, no grounds on half of the plugs, doubletaps, ect.... Time to call old Sparky!
ABI Home Services
Louisville Home Inspections
Louisville Home Inspectors



View Profile
Senior Member

Lafayette, Louisiana
Posts: 1103
Joined: Nov, 2009
Currently offline offline
  
Voltage drops reading on the suretest
[#6] Posted: Feb 04 2010 - 10:14:32 AM
Reply with Quote
Quote: That is one of the problems (not really a problem, but just too much information) with a ShureTest tester. I use to report voltage drops, but I got so tired of electricians saying that they could not really do anyting about it because it was an issue with the utility company. Then everyone would look at me for an answer.


A while back, there was a thread about feeding sub-panels from other sub-panels. That's one type of wiring practice that can result in voltage drop issues because the impedances add up. But the utility? Not a chance. Need another electrician. If you still think it's the utility, check the voltage drop on an outlet that is very near, or attached to the main panelboard.

I've never bothered with checking voltage drops but my eye is always on the lookout for light bulbs that suddenly dim for a few seconds. When I see it, the focus of the inspection is adjusted a little closer towards the electrical installation.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
Member

Denver, CO
Posts: 115
Joined: Dec, 2005
Currently offline offline
  
Voltage drops reading on the suretest
[#7] Posted: Feb 05 2010 - 07:37:22 AM
Reply with Quote
Quote: Originally posted by Ben H

I had a bathroom the other day with 12.8vd @20amp. The house had many other eletrical issues as well, no grounds on half of the plugs, doubletaps, ect.... Time to call old Sparky!


Chances are good that Sparky won't have a clue. The voltage drop provisions are an unenforceable "fine print note" in the NEC. I used to routinely measure voltage drops of 10-20% before my Suretest got stolen.

My advice is to throw away your Suretest.

View Profile
Active Member

Louisville, KY
Posts: 466
Joined: Jan, 2010
Currently offline offline
  
Voltage drops reading on the suretest
[#8] Posted: Feb 05 2010 - 10:37:02 AM
Reply with Quote
Quote: Originally posted by Garet

Quote: Originally posted by Ben H

I had a bathroom the other day with 12.8vd @20amp. The house had many other eletrical issues as well, no grounds on half of the plugs, doubletaps, ect.... Time to call old Sparky!


Chances are good that Sparky won't have a clue. The voltage drop provisions are an unenforceable "fine print note" in the NEC. I used to routinely measure voltage drops of 10-20% before my Suretest got stolen.

My advice is to throw away your Suretest.


I was referring to the rest of the issue's not the VD. Besides, wouldn't selling it be a better route?

ABI Home Services
Louisville Home Inspections
Louisville Home Inspectors



Member

Philly, PA
Posts: 175
Joined: May, 2008
Currently offline offline
  
Voltage drops reading on the suretest
[#9] Posted: Feb 05 2010 - 7:22:19 PM
Reply with Quote
If you eliminate voltage drop, the suretest is basically giving you the same info as a 10$ 3 lite tester.
View Profile
Associate Editor - TIJ

Charlestown, Massachusetts
Posts: 1399
Joined: Sep, 2003
Currently offline offline
  
Voltage drops reading on the suretest
[#10] Posted: Feb 05 2010 - 7:30:27 PM
Reply with Quote
No, that's not so. Suretests just give more information than the average HI -or electrician for that matter- can accurately interpret. They're good, but like a hammerdrill, they're just not great tools for HI's.

Jimmy

View Profile
Member

louisville, ne
Posts: 153
Joined: Feb, 2010
Currently offline offline
  
Voltage drops reading on the suretest
[#11] Posted: Feb 07 2010 - 6:29:07 PM
Reply with Quote
Do any of you guys check the voltage at the main coming into the panel? that would tell you which side the voltage drop is coming from,or am I thinking like a contractor again?
http://hyetechutilities .com
View Profile
Senior Member

Lafayette, Louisiana
Posts: 1103
Joined: Nov, 2009
Currently offline offline
  
Voltage drops reading on the suretest
[#12] Posted: Feb 07 2010 - 6:40:39 PM
Reply with Quote
Quote: Do any of you guys check the voltage at the main coming into the panel? that would tell you which side the voltage drop is coming from,or am I thinking like a contractor again?


Relax Jim. We're both contractors.

You're right on cue about checking voltage drop near the panel to get an idea how much of the impedance at a problem VD location is due to the premises wiring and how much is due to utility line impedance.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Administrator

Chicago, IL
Posts: 5930
Joined: Dec, 2003
Currently offline offline
  
Voltage drops reading on the suretest
[#13] Posted: Feb 07 2010 - 8:08:10 PM
Reply with Quote
This is one of those things that's not enforceable (per Garet's explanation), so is it a defect? Is there anything we can go to that says it's a real problem?

Not really.

I stopped reporting it years ago. Every house has it, at least every house I've looked at.




Kurt in Chicago
Workin' the Inner City

"Things are more like they are now than they ever have been before"
Dwight D. Eisenhower
View Profile
Editor - TIJ

Kenmore, WA
Posts: 12154
Joined: Dec, 2003
Currently online online
  
Voltage drops reading on the suretest
[#14] Posted: Feb 07 2010 - 9:30:59 PM
Reply with Quote
I wouldn't toss the SureTest. It comes in really handy when you have a house with aluminum wiring for pinpointing excessively high voltage drop that can indicate a corroded copper-to-aluminum connection.

ONE TEAM - ONE FIGHT!!!

Mike

View Profile
Administrator

Chicago, IL
Posts: 5930
Joined: Dec, 2003
Currently offline offline
  
Voltage drops reading on the suretest
[#15] Posted: Feb 07 2010 - 9:56:44 PM
Reply with Quote
True, but if I find aluminum wiring, I'm already going into danger mode and will be recommending all sorts of things.

I really don't need the Suretest to tell me that. And yes, I do have a carry a Suretest. Use it every day. Just not for determining voltage drop.

Kurt in Chicago
Workin' the Inner City

"Things are more like they are now than they ever have been before"
Dwight D. Eisenhower
View Profile
Senior Member

Gervais, Oregon
Posts: 1197
Joined: Jul, 2006
Currently offline offline
  
Voltage drops reading on the suretest
[#16] Posted: Feb 07 2010 - 10:10:38 PM
Reply with Quote
Maybe it's just mine, but I don't trust the suretest. It often seems to give me bogus readings.

One of my plans this year is to spend more time looking at a homes electrical system under load with my IR camera. I wonder what correlation exists between what the suretest says vrs infrared?

My guess is the correlation is poor.

Chris, Oregon

   
Previous Topic: Bought Another Fenix - Topic - Next Topic: Fluke 62 New TopicReply to TopicShare Topic Printer FriendlyBookmark this Topic
Jump To:
The Inspector's Journal Forums © 2002-2010 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2009 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000