 Reversed polarity Outlets
Errors and Omissions Insurance for home inspectors, appraisers, agents, brokers and other real estate professionals.   
Previous Topic: Excessive voltage update - Topic - Next Topic: Square D double tap New TopicReply to TopicShare Topic Printer FriendlyBookmark this Topic
Posted By  
Starting Member
erwin, tn
Posts: 14
Joined: Jan, 2010
Currently offline offline
  
Thread Start First Page
[#1] Posted: Mar 03 2010 - 9:03:05 PM
Reply with Quote
I inspected a 1981 year old house today and found that most all the 3 prong bedroom , living room and bathroom outlets were hot neutral reversed. Tested the outlets using a Ideal SureTest circuit tester. [ FOR YOUR INFO: The service panel had a plumbing ground.
I know hot neutral isn't correct, this would be a defect (Safety Issue) correct?? Just a bad electrician, or what?? Any thoughts


Click to View
Image Unavailable! Sorry you must be logged in to view images.
Click Here For Free Registration
17.3 KBThanks

View Profile
Senior Member

Newberg, OR
Posts: 1970
Joined: Mar, 2007
Currently offline offline
  
Reversed polarity Outlets
[#2] Posted: Mar 03 2010 - 9:15:17 PM
Reply with Quote
Safety defect for sure. You do understand why it is a safety concern don't you? (I read the post over at IN).

Bad electrician? I doubt it, but it's entirely possible. My guess is that someone replaced receptacle outlets at some point and had no clue.

Brandon

Portland Home Inspector
Starting Member
erwin, tn
Posts: 14
Joined: Jan, 2010
Currently offline offline
  
Reversed polarity Outlets
[#3] Posted: Mar 03 2010 - 9:18:48 PM
Reply with Quote
Quote: Originally posted by Brandon Whitmore

Safety defect for sure. You do understand why it is a safety concern don't you? (I read the post over at IN).

Bad electrician? I doubt it, but it's entirely possible. My guess is that someone replaced receptacle outlets at some point and had no clue.
Thanks for the info (Understand completely)

View Profile
Senior Member

Newberg, OR
Posts: 1970
Joined: Mar, 2007
Currently offline offline
  
Reversed polarity Outlets
[#4] Posted: Mar 03 2010 - 9:21:25 PM
Reply with Quote
Just in case anyone reading this down the road doesn't understand the safety implications, they can read this guy's blog:

http://activerain.com/blogsvie...a-hazard

Brandon

Portland Home Inspector
View Profile
Active Member

Swansea, IL
Posts: 806
Joined: Mar, 2006
Currently offline offline
  
Reversed polarity Outlets
[#5] Posted: Mar 04 2010 - 04:56:06 AM
Reply with Quote
I always say something like " The outlet located in the ... is wired incorrectly with the polarity reversed. This is a safety concern and needs to be corrected by a qualified individual."
Mark A. Perry
www.ahis1.com
View Profile
Senior Member

Collins, NY
Posts: 1485
Joined: Apr, 2008
Currently offline offline
  
Reversed polarity Outlets
[#6] Posted: Mar 04 2010 - 05:13:45 AM
Reply with Quote
This might be a little obvious but, only one receptacle in the circuit is likely reversed. Every receptacle down stream of it would be reverse polarity if they were wired correctly. If all the receptacles were reverse polarity I would blame the electrician, but since some of them are correct I think you have a few receptacles close to the upstream end of the circuits that were replaced and reversed.

Tom

Clear Creek Home Inspection, Collins, NY
View Profile
Active Member

Louisville, KY
Posts: 466
Joined: Jan, 2010
Currently online online
  
Reversed polarity Outlets
[#7] Posted: Mar 04 2010 - 08:24:02 AM
Reply with Quote
Quote: Originally posted by AHIS

I always say something like " The outlet located in the ... is wired incorrectly with the polarity reversed. This is a safety concern and needs to be corrected by a qualified individual."


Same here.

ABI Home Services
Louisville Home Inspections
Louisville Home Inspectors



Member

Victoria, British Columbia
Posts: 267
Joined: Nov, 2009
Currently offline offline
  
Reversed polarity Outlets
[#8] Posted: Mar 04 2010 - 5:49:42 PM
Reply with Quote
Quote: Originally posted by Tom Raymond

This might be a little obvious but, only one receptacle in the circuit is likely reversed. Every receptacle down stream of it would be reverse polarity if they were wired correctly. If all the receptacles were reverse polarity I would blame the electrician, but since some of them are correct I think you have a few receptacles close to the upstream end of the circuits that were replaced and reversed.

Tom
Right, Tom. Even if they were all wired backwards, only the first receptacle in each chain needs to be reversed to correct all those downstream, electrically that is. The hot wire could still be white though, which is wrong, so it's still best to get an electrician in there and check 'em all.

View Profile
Senior Member

Severna Park, Maryland
Posts: 2154
Joined: May, 2007
Currently offline offline
  
Reversed polarity Outlets
[#9] Posted: Mar 05 2010 - 05:13:40 AM
Reply with Quote
I avoid being specific about where polarity errors might originate. There could be a junction box hidden between walls somewhere that houses the deed. You just never know.

I identify the locations that I observed the polarity issues, mention the hazard and refer to the electrician to fix it.

John Dirks Jr - Arundel Home Inspection LLC - MD license: 29827
Maryland Home Inspectors - Maryland Home Inspection - Maryland Radon Testing - Baltimore County Rental Inspection
   
Previous Topic: Excessive voltage update - Topic - Next Topic: Square D double tap New TopicReply to TopicShare Topic Printer FriendlyBookmark this Topic
Jump To:
The Inspector's Journal Forums © 2002-2010 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.