Thread Start First Page [#1] Posted: Mar 06 2010 - 4:09:55 PM |  | |
|
Here is a first for me, Main Electrical panel is approximately 10' up from landing below. Easily accessible from side entry. I read in past posts some conflicting info. on minimum heights. From what I read 6' 7" is max. height to top of panel. Is this correct?
Click to View Image Unavailable! Sorry you must be logged in to view images. Click Here For Free Registration 20.62 KB
|
Mike O'Brien
|
|
|
| |
 Associate Editor - TIJ
    
|
Gaston, Oregon Posts: 5386
Joined: Dec, 2003
| offline |
|
|
|
| |
 Senior Member
   
|
Kenmore, WA Posts: 1747
Joined: Sep, 2004
| offline |
|
|
|
| |
 New Member

|
Kirkland, WA Posts: 32
Joined: Jan, 2009
| offline |
|
|
|
| |
 Senior Member
   
|
Kenmore, WA Posts: 1747
Joined: Sep, 2004
| offline |
|
Main panel height
[#5] Posted: Mar 06 2010 - 5:22:13 PM |  | |
|
Cool.
The folks wanted to do a 203k renovation project.
It was too much, too expensive. . .
|
Randy Navarro http://www.thecompleteinspection.com |
| |
|
|
| |
Member
 
|
Chestertown, MD Posts: 85
Joined: Apr, 2009
| offline |
|
Main panel height
[#6] Posted: Mar 07 2010 - 1:38:05 PM |  | |
|
While you say the panel is accessible from the side there is no way it will meet the workspace requirements in Article 110.
|
| |
|
|
| |
 Associate Editor - TIJ
    
|
Seattle, WA Posts: 1946
Joined: Dec, 2003
| offline |
|
Main panel height
[#7] Posted: Mar 07 2010 - 3:16:01 PM |  | |
|
I've got $100 that says it will never get changed or moved. No argument at all that it's wrong and should be reported as such but, "off the record", how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner. If it ever actually needs to be worked on, presumably a temporary safe workspace platform could be fashioned.
If this was my own home, my only real-life concern would be what the next home inspector would say when I sold it.
But...to repeat myself, it is wrong!
|
Richard Moore Rest Assured Inspection Services Seattle, WA http://www.rainspect.com
|
| |
|
|
| |
 Associate Editor - TIJ
    
|
Gaston, Oregon Posts: 5386
Joined: Dec, 2003
| offline |
|
|
|
| |
 Member
 
|
louisville, ne Posts: 153
Joined: Feb, 2010
| offline |
|
Main panel height
[#9] Posted: Mar 07 2010 - 4:13:17 PM |  | |
|
does anybody else think the floor was removed by previous lame brain remodeler?
|
| http://hyetechutilities .com |
| |
|
|
| |
Member
 
|
Dallas, GA Posts: 79
Joined: Feb, 2004
| offline |
|
Main panel height
[#10] Posted: Mar 07 2010 - 5:40:14 PM |  | |
|
That was the first thing I thought, remodel. Surely it was not installed that high originally.
|
| Tim M. |
| |
|
|
| |
Member
 
|
Chestertown, MD Posts: 85
Joined: Apr, 2009
| offline |
|
Main panel height
[#11] Posted: Mar 07 2010 - 5:45:01 PM |  | |
|
Quote: Originally posted by Jim KatenQuote: Originally posted by Jim Port
While you say the panel is accessible from the side there is no way it will meet the workspace requirements in Article 110.
Which part? I can't find anything in 110 that would prohibit this. - Jim Katen, Oregon
I doubt that many would think that 110.26 "to permit ready and safe operation and maintnance" would be meet. I would also challenge the depth of the workspace meeting the 36" depth if a ladder were used to gain access to work in the panel. I would also note that this could be argued that this is not dedicated space as required.
|
| |
|
|
| |
 Associate Editor - TIJ
    
|
Gaston, Oregon Posts: 5386
Joined: Dec, 2003
| offline |
|
|
|
| |
Member
 
|
Chestertown, MD Posts: 85
Joined: Apr, 2009
| offline |
|
Main panel height
[#13] Posted: Mar 08 2010 - 06:25:25 AM |  | |
|
I agree that 240.24(A) regarding the maximum height being exceeded would be the best site.
I was aware of 240.24(F), not over steps, but the OP said this was over a landing. In the Mike Holt "Changes to the NEC 2008" his analysis states that panel can be over landings. I would tend to agree. While the landing is part of the stairway it is not steps.
|
| |
|
|
| |
Member
 
|
Yakima, WA Posts: 166
Joined: Jan, 2009
| offline |
|
Main panel height
[#14] Posted: Mar 08 2010 - 08:24:53 AM |  | |
|
| Quote: Originally posted by Richard Moore
I've got $100 that says it will never get changed or moved. No argument at all that it's wrong and should be reported as such but, "off the record", how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner. If it ever actually needs to be worked on, presumably a temporary safe workspace platform could be fashioned.
If this was my own home, my only real-life concern would be what the next home inspector would say when I sold it.
But...to repeat myself, it is wrong!
I agree with Richard, yes its wrong.... I would certainly note it in the report.... my biggest concern would be as Richard said: 'how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner.' ??
Jerry [/quote]
|
| |
|
|
| |
 Associate Editor - TIJ
    
|
Gaston, Oregon Posts: 5386
Joined: Dec, 2003
| offline |
|
Main panel height
[#15] Posted: Mar 08 2010 - 10:17:10 AM |  | |
|
Quote: Originally posted by Jerry LozierQuote: Originally posted by Richard Moore
I've got $100 that says it will never get changed or moved. No argument at all that it's wrong and should be reported as such but, "off the record", how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner. If it ever actually needs to be worked on, presumably a temporary safe workspace platform could be fashioned.
If this was my own home, my only real-life concern would be what the next home inspector would say when I sold it.
But...to repeat myself, it is wrong!
I agree with Richard, yes its wrong.... I would certainly note it in the report.... my biggest concern would be as Richard said: 'how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner.' ?? Jerry
It's not an issue till something goes wrong. Then it's a big issue.
- Jim Katen, Oregon
|
| |
|
|
| |
Member
 
|
Dallas, GA Posts: 79
Joined: Feb, 2004
| offline |
|
Main panel height
[#16] Posted: Mar 08 2010 - 4:37:18 PM |  | |
|
It reminds me of the old houses with uneven stairs. You write it up because it's a safety concern, and to CYA. It is unlikely that anyone is going to rip out the stairs and rebuild. Same here. Write it up, CYA, and likely no one will move the panel.
|
| Tim M. |
| |
|
| |
|
|