[#1] Posted: 06/15/2011 - 07:45:11 AM
Reply with Quote
I found a 220v double 15amp breaker in panel (15+15 = 30amp)
toggles factory fastened with metal clip.

top lug connected to red wire
bottom lug connected to black wire
single neutral and ground wire leaving panel with red and black

duplex outlet under kitchen sink
top of outlet connected to black wire and neutral white
ground connected

bottom of outlet connected to red wire and common ground, and seperate white.

bottom used for plug and cord to disposer
top used for plug and cord to dishwasher

no photos, new construction, muni inspected, the folks are not happy when I told them I have never seen this.

Anyone see this on a regular basis?


Les
View Profile
Rochester, New York
Posts: 4367
Joined: Dec, 2003
Currently offline offline
  
Odd configuration?
[#2] Posted: 06/15/2011 - 08:43:55 AM
Reply with Quote
The separate neutral thing is rather unnerving; are you sure it wasn't pigtailed?


Other than that, I see multiwire branch circuits serving the dishwasher and disposal all the time.

Chad Fabry
StructureSmart Home Inspection Rochester, NY
www.structuresmart.com
View Profile
Kenmore, WA
Posts: 15733
Joined: Dec, 2003
Currently offline offline
  
Odd configuration?
[#3] Posted: 06/15/2011 - 08:53:42 AM
Reply with Quote
Yeah,

Sounds like a 15-amp MWBC to me. Like Chad says, I bet that 'separate' white is pigtailed back in the box. See disposals and dishwashers on the same MWBC all the time.

ONE TEAM - ONE FIGHT!!!

Mike

View Profile
DeWitt, Mi
Posts: 3633
Joined: Jan, 2004
Currently offline offline
  
Odd configuration?
[#4] Posted: 06/15/2011 - 09:03:12 AM
Reply with Quote
so the single throw will disconnect both? Wht is likely pigtailed. this is a condo sub panel, main is at meter three floors below.

Les
View Profile
Victoria, British Columbia
Posts: 3164
Joined: Nov, 2009
Currently offline offline
  
Odd configuration?
[#5] Posted: 06/15/2011 - 09:57:48 AM
Reply with Quote
Up until recently, all Canadian counter outlets were wired that way - 15 amp split duplex*.
The tab on the hot side of the receptacle is snapped off to separate the top from the bottom. On the neutral side of the receptacle, the tab is left in place, so one neutral connection supplies top and bottom.
Les, since each leg supplies only one receptacle, you have two 120 volt, 15 amp supplies there. They are tied together to reduce the chance of a shock, safety issue for Sparky.

The new rules (CEC 2006) allow 20 amp so that people can have unsplit GFCI outlets around the sink.

www.allsafehome.ca
View Profile
DeWitt, Mi
Posts: 3633
Joined: Jan, 2004
Currently offline offline
  
Odd configuration?
[#6] Posted: 06/15/2011 - 12:40:13 PM
Reply with Quote
Thanks John, guess I knew that, but in this area we have not seen the breakers tied together at the panel
thanks guys!

Les
View Profile
Newberg, OR
Posts: 2866
Joined: Mar, 2007
Currently offline offline
  
Odd configuration?
[#7] Posted: 06/15/2011 - 12:57:33 PM
Reply with Quote
Quote: Thanks John, guess I knew that, but in this area we have not seen the breakers tied together at the panel
thanks guys!



Hasn't it been an NEC requirement for years? Of course, I don't know what code MI falls under.


Brandon

Portland Home Inspector
Chestertown, MD
Posts: 256
Joined: Apr, 2009
Currently offline offline
  
Odd configuration?
[#8] Posted: 06/15/2011 - 1:33:31 PM
Reply with Quote
A double pole 15 is not a 30 amp breaker. It is a 15 amp breaker.

There should have been no reason to break the tab on the neutral side.

View Profile
DeWitt, Mi
Posts: 3633
Joined: Jan, 2004
Currently offline offline
  
Odd configuration?
[#9] Posted: 06/15/2011 - 3:18:09 PM
Reply with Quote
Quote: Originally posted by Jim Port

A double pole 15 is not a 30 amp breaker. It is a 15 amp breaker.

There should have been no reason to break the tab on the neutral side.

agreed!

Les
View Profile
Gaston, Oregon
Posts: 8897
Joined: Dec, 2003
Currently offline offline
  
Odd configuration?
[#10] Posted: 06/15/2011 - 5:10:16 PM
Reply with Quote
Quote: Originally posted by Les

Thanks John, guess I knew that, but in this area we have not seen the breakers tied together at the panel
thanks guys!



That's because it wasn't required until the 2008 NEC. Before that, the breakers didn't need a tie bar. Without a tie bar, it wouldn't have shown up on your radar.

Jim Katen, Oregon
www.amipdx.com
   
Previous Topic: What kind of outlets? - Topic - Next Topic: Safe per the NEC (or not) New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000