[#1] Posted: 01/05/2012 - 4:20:31 PM
Reply with Quote
I recently had my oil furnace and ductwork replaced in my home after my existing furnace malfunctioned and filled the entire house full of white smoke. I am concerned because my flue seems to have white corrosive growth and water coming out of the seams of the metal and on the inside of the flue. I have attache photos showing the corrosion after approx 2 1/2 weeks of use. I had my chimney cleaned by a local chimney sweeping company and expressed concern of the corrosive growth and they don't seem to think this is a big thing to worry about however I am a little skeptical after ready a few articles online. I was told my chimney does not have a metal liner but rather is made of clay. If I am looking at a potential problem in the near future I would like to have this fixed immediately rather than waiting until damage is done. Am I over worrying about the water and corrosion or should I find a different contractor?

State College, PA
Posts: 9
Joined: Jan, 2012
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#2] Posted: 01/05/2012 - 4:25:22 PM
Reply with Quote


Click to View

50.53 KB



Click to View

36.31 KB

View Profile
State: PA & NJ
Posts: 3208
Joined: Jan, 2004
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#3] Posted: 01/05/2012 - 4:31:47 PM
Reply with Quote
Pictures usually don't appear because of spaces in the file name.

The white deposits are probably from condensation. It's a sign that combustion byproducts are cooling in the vent connector or in the vertical chimney flue too soon. It can be from a number of reasons. One possibility is that the new furnace output is cooler than the previous, requiring a smaller chimney flue so that the exhaust rises to the top of the chimney before cooling.

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
View Profile
State: PA & NJ
Posts: 3208
Joined: Jan, 2004
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#4] Posted: 01/05/2012 - 4:33:18 PM
Reply with Quote
Now that the pics are posted, is that vent connector increased in diameter, just before entering the chimney thimble?
Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
State College, PA
Posts: 9
Joined: Jan, 2012
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#5] Posted: 01/05/2012 - 4:36:12 PM
Reply with Quote
Quote: Originally posted by Bill Kibbel

Pictures usually don't appear because of spaces in the file name.

The white deposits are probably from condensation. It's a sign that combustion byproducts are cooling in the vent connector or in the vertical chimney flue too soon. It can be from a number of reasons. One possibility is that the new furnace output is cooler than the previous, requiring a smaller chimney flue so that the exhaust rises to the top of the chimney before cooling.


The furnace I had installed was rated at 85% efficient oil furnace as compared to the older one which was 78%.

State College, PA
Posts: 9
Joined: Jan, 2012
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#6] Posted: 01/05/2012 - 4:41:07 PM
Reply with Quote
Quote: Originally posted by Bill Kibbel

Pictures usually don't appear because of spaces in the file name.

The white deposits are probably from condensation. It's a sign that combustion byproducts are cooling in the vent connector or in the vertical chimney flue too soon. It can be from a number of reasons. One possibility is that the new furnace output is cooler than the previous, requiring a smaller chimney flue so that the exhaust rises to the top of the chimney before cooling.

Yes, I measured the flue pipe prior to the transition piece to be 5" dia. and the metal piece in chimney is 6.1" dia.

View Profile
Gaston, Oregon
Posts: 8080
Joined: Dec, 2003
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#7] Posted: 01/05/2012 - 4:43:50 PM
Reply with Quote
Quote: Originally posted by Bill Kibbel

Pictures usually don't appear because of spaces in the file name.

The white deposits are probably from condensation. It's a sign that combustion byproducts are cooling in the vent connector or in the vertical chimney flue too soon. It can be from a number of reasons. One possibility is that the new furnace output is cooler than the previous, requiring a smaller chimney flue so that the exhaust rises to the top of the chimney before cooling.


Another possibility is that the furnace is too large. The resulting short cycles don't allow the flue to fully warm.

Jim Katen, Oregon
www.amipdx.com
State College, PA
Posts: 9
Joined: Jan, 2012
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#8] Posted: 01/05/2012 - 5:43:59 PM
Reply with Quote
What would you guys suggest I do?
Northville, New York
Posts: 116
Joined: Feb, 2004
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#9] Posted: 01/05/2012 - 7:32:28 PM
Reply with Quote
I'll bet that:

1. not only is the furnace more efficient but, the firing rate is less.

2. the chimney is located on the exterior of the building.

As has been stated, condensation is occurring inside the flue. The flue will need to be made smaller and easier to heat. This will involve the installation of a properly sized stainless steel liner inside the masonry chimney.

As Jim Katen mentioned, make sure that the furnace is not short cycling.

Tom Corrigan, Ret.

Lansdale, pa
Posts: 7
Joined: May, 2009
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#10] Posted: 01/05/2012 - 8:23:53 PM
Reply with Quote
Another thing to look at is whether the chimney flue extends below the flue connector. That allows some condensation to collect at the bottom and evaporate when the flue is hot. Sometimes that space gets filled with soot or debris.
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#11] Posted: 01/05/2012 - 9:08:57 PM
Reply with Quote
How about a picture of the rest of the install,including where flue attaches to furnace?
State College, PA
Posts: 9
Joined: Jan, 2012
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#12] Posted: 01/06/2012 - 6:42:41 PM
Reply with Quote
Quote: Originally posted by plummen

How about a picture of the rest of the install,including where flue attaches to furnace?


Here are some more photos showing the rest of the furnace and flue
Click to View

48.2 KB

Click to View

40.18 KB

Click to View

82 KB

Click to View

64.52 KB

View Profile
State: PA & NJ
Posts: 3208
Joined: Jan, 2004
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#13] Posted: 01/06/2012 - 7:51:27 PM
Reply with Quote
The vent connector is very long with several elbows. Combine that with the increase in it's dimension, prior to the termination at the vertical chimney flue, is likely the primary cause of the condensation. (Do the horizontal sections slope the right way?)

They probably put the sealant and tape on the joints of the vent connector because combustion byproducts, having already cooled before rising up the chimney, were spilling out. A properly installed natural-draft vent system needs nothing added to the joints and nothing leaks out.

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#14] Posted: 01/06/2012 - 10:25:01 PM
Reply with Quote
Quote: Originally posted by Bill Kibbel

The vent connector is very long with several elbows. Combine that with the increase in it's dimension, prior to the termination at the vertical chimney flue, is likely the primary cause of the condensation. (Do the horizontal sections slope the right way?)

They probably put the sealant and tape on the joints of the vent connector because combustion byproducts, having already cooled before rising up the chimney, were spilling out. A properly installed natural-draft vent system needs nothing added to the joints and nothing leaks out.

Here I go agreeing with the home inspector again!
The first piece of pipe after the 90 coming out of the furnace is running down hill,then it looks like its running flat to the next 90.
Then it must start climbing at some point to hit the chimney going out.
Why didnt they take and spin the furnace 90 degrees when they installed it to atleast cut down on the offsets?
With that many offsets its no wonder they needed that big of a flue pipe to vent it,but by the time it reaches the chimney im suprised it has enough force behind it to properly vent!
And as far as the aluminum tape on the flue pipe it must be to keep all the condensation from dripping out of all the joints in that flat/reversed sloping pipe!

Northville, New York
Posts: 116
Joined: Feb, 2004
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#15] Posted: 01/07/2012 - 08:55:52 AM
Reply with Quote

Here I go agreeing with a contractor but,

Note also that the minimum required clearance between the single wall smoke pipe and the plastic condensate drain, the plastic plumbing waste pipe and (if the code guy is on his game) the combustible refrigerant tube insulation is required to be at least 18"!

You will need to install a type L smoke pipe and/or change to non-combustible pipes and insulation.

Tom Corrigan

State College, PA
Posts: 9
Joined: Jan, 2012
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#16] Posted: 01/07/2012 - 2:10:03 PM
Reply with Quote
Quote: Originally posted by Tom Corrigan


Here I go agreeing with a contractor but,

Note also that the minimum required clearance between the single wall smoke pipe and the plastic condensate drain, the plastic plumbing waste pipe and (if the code guy is on his game) the combustible refrigerant tube insulation is required to be at least 18"!

You will need to install a type L smoke pipe and/or change to non-combustible pipes and insulation.

Tom Corrigan


Thank you all for you posts as they have been very helpful. I have contacted a local inspector and he mentioned that as of 2004 my contractor was required to obtain a permit to replace the furnace and duct work which would have required a inspection prior and after the installation. I suspect the contractor has not obtained the proper permits since I have not received any information about a permit and no code inspection was done prior to the work being started. I'm going to contact my local code office monday to schedule an inspection and find out if any permits were obtained.

View Profile
Crystal Lake, IL
Posts: 1174
Joined: Sep, 2003
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#17] Posted: 01/07/2012 - 2:19:07 PM
Reply with Quote
Quote: Originally posted by Tom Corrigan


Here I go agreeing with a contractor but,

Tom Corrigan

Uhm, where are your bouncing smiley-faces?

View Profile
Dallas, TX
Posts: 1072
Joined: Oct, 2006
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#18] Posted: 01/07/2012 - 2:57:03 PM
Reply with Quote
Quote: Originally posted by Jerry Simon

Quote: Originally posted by Tom Corrigan


Here I go agreeing with a contractor but,

Tom Corrigan

Uhm, where are your bouncing smiley-faces?


When you reply click on the "Show Entire Smile List"

I just tried it as I didn't know where they were either.


Cheers,

Nolan E. Kienitz
Nolan's Inspections, LLC
Dallas Home Inspections
http://www.NolansInspections.com
View Profile
Ridgewood, NJ
Posts: 949
Joined: Sep, 2002
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#19] Posted: 01/08/2012 - 3:28:50 PM
Reply with Quote
Quote: Originally posted by Tom Corrigan

Note also that the minimum required clearance between the single wall smoke pipe and the plastic condensate drain, the plastic plumbing waste pipe and (if the code guy is on his game) the combustible refrigerant tube insulation is required to be at least 18"!
Tom Corrigan

Some newer oil fired units have a requirement for only 9 inches clearance from the single wall flue pipe.

Neal Lewis
www.totalhomeinspectionservices.com
New Cumberland, PA
Posts: 5
Joined: Sep, 2011
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#20] Posted: 01/11/2012 - 11:37:51 AM
Reply with Quote
Why does the floor appear wet?
View Profile
louisville, ne
Posts: 354
Joined: Feb, 2010
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#21] Posted: 01/11/2012 - 11:53:06 AM
Reply with Quote
Probably all the water leaking past the red rtv hes got slopped all over the joints on the single wall fittings!
Alexandria, Virginia
Posts: 11
Joined: Mar, 2012
Currently offline offline
  
New Furnace and Flue with corrosion after 2 weeks
[#22] Posted: 03/14/2012 - 11:36:45 PM
Reply with Quote
First things first guys, this is an oil furnace which requires tuning to set the air fuel mix and dial in the stack temp to ensure condensation doesnt occur in chimney. The first thing that should be done is a combustion analisys by an oil tech and make sure the burner is set up properly. Oil is not like a gas unit ( plug and play) it must be tuned up annually. One can make many adjustments from O2 levels, oil pressure, and oil flow rate, all of which affect stack temps therefore the potential for condensation. I wont touch an oil burner without performing combustion analisys.


Or could be rain water infiltration

Install notes; the exhaust/ flue piping MUST always have a positive pitch, yours does not and this is a major concern! around here its against code to add sealant or tape to metal flue piping as its not needed therefore is used to conceal a problem.. Get a good oil tech out to inspect/correct installation.

   
Previous Topic: Is this some sort of new fangled S-trap? - Topic - Next Topic: heat pump thermostat New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000