[#1] Posted: 03/24/2012 - 5:22:20 PM
Reply with Quote
As you can see the ground wires from numerous circuits are twisted together and a single pigtail (from each group) is running to the grounding/neutral bus bar. Since I have not seen this before (that I can remember) I assume it is wroung. Can someone confirm this is wrong. If it is wrong I'm trying to figure out why it is wrong seems it should work???

Click to View

57.14 KB

Click to View

86.5 KB

Mark A. Perry
www.ahis1.com
View Profile
Severna Park, Maryland
Posts: 3458
Joined: May, 2007
Currently offline offline
  
Grounds
[#2] Posted: 03/24/2012 - 5:47:38 PM
Reply with Quote
If a charge needs to find ground I doubt the electricity itself would know the difference. I'd like to hear the response from the gurus as well. I'd be uncomfortable just saying it's fine as is.
John Dirks Jr - Arundel Home Inspection LLC - MD license: 29827
Maryland Home Inspectors - Maryland Home Inspection - Maryland Radon Testing - Baltimore County Rental Inspection
View Profile
Reisterstown, Maryland
Posts: 265
Joined: Apr, 2011
Currently offline offline
  
Grounds
[#3] Posted: 03/24/2012 - 6:24:21 PM
Reply with Quote
If, instead of grounds, these were 'hot' or 'neutral wires, would it be more wrong?

Why do we use wire nuts to make connections?

Why is the integrity of connections between ground conductors less important than the connections between un-grounded conductors?

Could this be really 'sloppy work?'

Bob Kenney
www.IndependentHomeInspectionMD.com
"We are masters of the unspoken word, and slaves to those we speak." Winston Churchill
View Profile
Kenmore, WA
Posts: 15393
Joined: Dec, 2003
Currently offline offline
  
Grounds
[#4] Posted: 03/24/2012 - 7:01:01 PM
Reply with Quote
It's jackleg work.

Where's the bond to the neutral bus?

He didn't have enough room on that bus for all of the grounded conductors as well as the equipment grounding conductors and he was too lazy to install a bus to handle the excess equipment grounding conductors. Ask yourself if that's been done in a workmanlike manner and if not write it up and call it was it is - a rat's nest.

ONE TEAM - ONE FIGHT!!!

Mike

View Profile
Lafayette, Louisiana
Posts: 3853
Joined: Nov, 2009
Currently offline offline
  
Grounds
[#5] Posted: 03/24/2012 - 7:35:15 PM
Reply with Quote
A compression connector is needed. Twisting alone is insufficient.

Quote: E3306.10 Splices. Conductors shall be spliced or joined with splicing devices listed for the purpose. Splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device listed for the purpose. Wire connectors or splicing means installed on conductors for direct burial shall be listed for such use.


Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Severna Park, Maryland
Posts: 3458
Joined: May, 2007
Currently offline offline
  
Grounds
[#6] Posted: 03/25/2012 - 05:31:18 AM
Reply with Quote
Quote: Originally posted by Marc

A compression connector is needed. Twisting alone is insufficient.

Quote: E3306.10 Splices. Conductors shall be spliced or joined with splicing devices listed for the purpose. Splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device listed for the purpose. Wire connectors or splicing means installed on conductors for direct burial shall be listed for such use.


Marc


Yup, with the proper connector and as long as the single conductor that connects to the buss is not smaller than any of the individual ones in the bundle, it would be acceptable by code, correct?

John Dirks Jr - Arundel Home Inspection LLC - MD license: 29827
Maryland Home Inspectors - Maryland Home Inspection - Maryland Radon Testing - Baltimore County Rental Inspection
View Profile
Seattle, WA
Posts: 2516
Joined: Dec, 2003
Currently offline offline
  
Grounds
[#7] Posted: 03/25/2012 - 06:28:16 AM
Reply with Quote
Quote: Originally posted by rkenney

If, instead of grounds, these were 'hot' or 'neutral wires, would it be more wrong?
You could overload and fry a neutral pigtail, but current caused by a ground fault should be momentary and quickly trip the breaker. So, yeah, it would be "more wrong" for a hot or neutral.

Quote: Why do we use wire nuts to make connections?
Like others have mentioned, I would be comfortable with a compression sleeve at the twisted areas.

Quote: Why is the integrity of connections between ground conductors less important than the connections between un-grounded conductors?
Both are important but see above.

Quote: Could this be really 'sloppy work?'
I think we have all seen much, much worse!

Richard Moore
Rest Assured Inspection Services
Seattle, WA
http://www.rainspect.com
View Profile
Lafayette, Louisiana
Posts: 3853
Joined: Nov, 2009
Currently offline offline
  
Grounds
[#8] Posted: 03/25/2012 - 06:50:08 AM
Reply with Quote
Quote: Originally posted by John Dirks Jr
Yup, with the proper connector and as long as the single conductor that connects to the buss is not smaller than any of the individual ones in the bundle, it would be acceptable by code, correct?

If the conductors are properly sized and the connector is listed for the purpose, yes, as far as I know.

I'm not sure if you'll find a connector that's listed to receive a dozen or so EGC's that are twisted together that way.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Reisterstown, Maryland
Posts: 265
Joined: Apr, 2011
Currently offline offline
  
Grounds
[#9] Posted: 03/25/2012 - 07:39:49 AM
Reply with Quote
Quote: Originally posted by Richard Moore

Quote: Originally posted by rkenney

If, instead of grounds, these were 'hot' or 'neutral wires, would it be more wrong?

You could overload and fry a neutral pigtail, but current caused by a ground fault should be momentary and quickly trip the breaker. So, yeah, it would be "more wrong" for a hot or neutral.

Point is, wrong is wrong. Write it up.

Why do we use wire nuts to make connections?

Like others have mentioned, I would be comfortable with a compression sleeve at the twisted areas.

So, you should be uncomfortable? Write it up.

Why is the integrity of connections between ground conductors less important than the connections between un-grounded conductors?

Both are important but see above.

I see alot of loose ground conductors. If not now, when? Write it up.

Could this be really 'sloppy work?'

I think we have all seen much, much worse!

I'm not going to write that in the report, and neither are you. If the panel looks like this, lots of room to work and an easy fix, what's the rest of the wiring look like? Just write it up


Bob Kenney
www.IndependentHomeInspectionMD.com
"We are masters of the unspoken word, and slaves to those we speak." Winston Churchill
View Profile
Swansea, IL
Posts: 1352
Joined: Mar, 2006
Currently offline offline
  
Grounds
[#10] Posted: 03/25/2012 - 08:08:54 AM
Reply with Quote
Good Discussion guys - thanks and enjoy the rest of your weekend.
Mark A. Perry
www.ahis1.com
View Profile
Gaston, Oregon
Posts: 8083
Joined: Dec, 2003
Currently offline offline
  
Grounds
[#11] Posted: 03/25/2012 - 11:18:13 AM
Reply with Quote
Quote: Originally posted by Mark P

As you can see the ground wires from numerous circuits are twisted together and a single pigtail (from each group) is running to the grounding/neutral bus bar. Since I have not seen this before (that I can remember) I assume it is wroung. Can someone confirm this is wrong.

It's wrong.

Quote: If it is wrong I'm trying to figure out why it is wrong seems it should work???

It's wrong because twisting wires together is not a recognized form of splicing (110.14(B)).

I'd also argue that it's wrong because you can't isolate one circuit without interrupting the grounding continuity of other circuits.



Jim Katen, Oregon
www.amipdx.com
View Profile
Marin County, CA
Posts: 342
Joined: Mar, 2002
Currently offline offline
  
Grounds
[#12] Posted: 03/26/2012 - 9:30:50 PM
Reply with Quote
408.40 in the NEC requires a terminal bar for the equipment grounding conductors. The panel manufacturers do not always supply a separate equipment ground bar, since the same panel might be used as service equipment where the equipment grounds and neutrals could go on the same bar. They do make separate terminal bars that are easily added to a panel like this one.

While it is not likely to have any effect on the electrical performance of this piece of equipment, allowing a thing like this to pass is the first step on a slippery slope. It is the signature of someone who did not know how to wire a panel. It should be corrected by a real electrician.


Douglas Hansen
www.codecheck.com
   
Previous Topic: Al branch circuits werent expected here - Topic - Next Topic: receptacle placement New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000