Thermal Magnetic Breaker Settings

Previous Topic: large splices in panel - Topic - Next Topic: Square D  AFCI breaker double tapped New TopicReply to TopicShare Topic
Posted By  
View Profile
Evergreen Park (Chicago), IL
Posts: 1539
Joined: Apr, 2004
Currently offline offline
  
Thread Start First Page
[#1] Posted: 04/02/2012 - 08:51:39 AM
Reply with Quote
This main disconnect has adjustable dials. What are they for and does a homeowner need any knowledge about their settings? Or do I for that matter?

I suppose they are for some sensitivity response to over loads but I'm guessing.

Click to View

68.9 KB
Click to View

34.78 KB

Mike Lamb
http://www.inspection2020.com/
View Profile
Gaston, Oregon
Posts: 8080
Joined: Dec, 2003
Currently offline offline
  
Thermal Magnetic Breaker Settings
[#2] Posted: 04/02/2012 - 09:19:21 AM
Reply with Quote
Perhaps an adjustable time delay?
Jim Katen, Oregon
www.amipdx.com
View Profile
Lafayette, Louisiana
Posts: 3840
Joined: Nov, 2009
Currently offline offline
  
Thermal Magnetic Breaker Settings
[#3] Posted: 04/02/2012 - 4:13:24 PM
Reply with Quote
I think the adjustment on the left is there for the factory to set the magnetic trip I(m), characteristics of the breaker to whatever it's supposed to be for that particular panel. This particular adjustment seems capable of reaching values of anything between 5 and 10 times the value of the thermal trip, I(n). I don't think it's there for the homeowner or even the electrician to play with. If you look at the label, it might tell you just what value of I(m) the adjustment is supposed to be set at.

I don't know what the adjustment on the right side is for. A better view might help.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
Allen, Texas
Posts: 532
Joined: Dec, 2006
Currently offline offline
  
Thermal Magnetic Breaker Settings
[#4] Posted: 04/02/2012 - 4:15:13 PM
Reply with Quote
I've never seen it but then at 400 amps, that in itself would be a rareity.
Jim Luttrall
Mr. Inspector.net, Inc.
www.mrinspector.net
View Profile
State: PA & NJ
Posts: 3208
Joined: Jan, 2004
Currently offline offline
  
Thermal Magnetic Breaker Settings
[#5] Posted: 04/03/2012 - 4:12:35 PM
Reply with Quote
They are breakers manufactured for industrial equipment. The dials are to make adjustments to the breakers to match the characteristics of industrial motors. In other words, to minimize nuisance tripping on motor start-up.
Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
View Profile
Evergreen Park (Chicago), IL
Posts: 1539
Joined: Apr, 2004
Currently offline offline
  
Thermal Magnetic Breaker Settings
[#6] Posted: 04/03/2012 - 10:55:23 PM
Reply with Quote
This is in a house with nothing electrically special going on.

100 amp main panel would be just fine.

Mike Lamb
http://www.inspection2020.com/
   
Previous Topic: large splices in panel - Topic - Next Topic: Square D  AFCI breaker double tapped New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000