Overfull panel

Previous Topic: Doube Taps - Topic - Next Topic: GECs On EGC Bars - Not Service Neutral Bar New TopicReply to TopicShare Topic
Posted By  
View Profile
Swansea, IL
Posts: 1352
Joined: Mar, 2006
Currently offline offline
  
Thread Start First Page
[#1] Posted: 04/15/2012 - 08:01:43 AM
Reply with Quote
I am just wanting to confirm that this panel (GE PowerMark Gold - TM 2010) does not permit the use of tandum breakers and it is in fact overfull.

Click to View

77.36 KB

Click to View

92.54 KB

Thanks You


Click to View

38.04 KB

Mark A. Perry
www.ahis1.com
View Profile
Lafayette, Louisiana
Posts: 3859
Joined: Nov, 2009
Currently offline offline
  
Overfull panel
[#2] Posted: 04/15/2012 - 08:47:36 AM
Reply with Quote
Did you mean Tandem or Duplex?

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Swansea, IL
Posts: 1352
Joined: Mar, 2006
Currently offline offline
  
Overfull panel
[#3] Posted: 04/15/2012 - 08:59:39 AM
Reply with Quote
UMM - is there a difference?
Mark A. Perry
www.ahis1.com
View Profile
Evergreen Park (Chicago), IL
Posts: 1540
Joined: Apr, 2004
Currently offline offline
  
Overfull panel
[#4] Posted: 04/15/2012 - 09:19:15 AM
Reply with Quote
http://www.ashireporter.org/ar...?id=2047

You are right. Tandems should not be used in this panel.

Mike Lamb
http://www.inspection2020.com/
View Profile
Lafayette, Louisiana
Posts: 3859
Joined: Nov, 2009
Currently offline offline
  
Overfull panel
[#5] Posted: 04/15/2012 - 09:28:47 AM
Reply with Quote
I think of tandem as one 2-pole breaker and duplex as 2 single-pole breakers in one slot.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Swansea, IL
Posts: 1352
Joined: Mar, 2006
Currently offline offline
  
Overfull panel
[#6] Posted: 04/15/2012 - 09:36:27 AM
Reply with Quote
Quote: Originally posted by Marc

I think of tandem as one 2-pole breaker and duplex as 2 single-pole breakers in one slot.

Marc


I see - I am referring to 2 single pole breakers in one slot.

Mark A. Perry
www.ahis1.com
View Profile
Nazareth, PA
Posts: 1057
Joined: Apr, 2002
Currently offline offline
  
Overfull panel
[#7] Posted: 04/15/2012 - 09:53:24 AM
Reply with Quote
"20 poles maximum" is printed on the label. It's too bad all panelboards don't contain that info.
Joe Hancaviz
Nazareth, PA
View Profile
Gaston, Oregon
Posts: 8092
Joined: Dec, 2003
Currently offline offline
  
Overfull panel
[#8] Posted: 04/15/2012 - 12:40:36 PM
Reply with Quote
Quote: Originally posted by Inspectorjoe

"20 poles maximum" is printed on the label. It's too bad all panelboards don't contain that info.


I'd like to see the transform that produces 20 poles of power.

Why didn't they just say "20 breakers maximum."

Jim Katen, Oregon
www.amipdx.com
View Profile
Seattle, WA
Posts: 2516
Joined: Dec, 2003
Currently offline offline
  
Overfull panel
[#9] Posted: 04/15/2012 - 1:18:37 PM
Reply with Quote
Quote: Originally posted by Jim Katen



Why didn't they just say "20 breakers maximum."

Well, then you would have some arguing that the 240 vac breaker for the range is just a single breaker. Johnny Homeowner buys and installs a "single" breaker, no matter how many poles it might have. The number of poles may still be a bit confusing, but perhaps it will at least get Bubba to ask questions.

Slight thread drift. I just discovered that the 42 circuit/pole max for panels has been largely removed with the 2008 NEC. 408.35 is no longer there.
See http://static.schneider-electr...0701.pdf

Richard Moore
Rest Assured Inspection Services
Seattle, WA
http://www.rainspect.com
View Profile
Kenmore, WA
Posts: 15397
Joined: Dec, 2003
Currently offline offline
  
Overfull panel
[#10] Posted: 04/15/2012 - 1:44:08 PM
Reply with Quote
It would be interesting to have the opp to pop one of those breakers to see if the bus has a rejection feature and if so whether the breaker had been modified; and if there is a rejection feature and the breaker wasn't modified, find out what type breaker is being used.

ONE TEAM - ONE FIGHT!!!

Mike

View Profile
Sykesville, Maryland
Posts: 312
Joined: Nov, 2009
Currently offline offline
  
Overfull panel
[#11] Posted: 04/15/2012 - 2:44:08 PM
Reply with Quote
You are correct, no tandems allowed. Panel is labeled 20 pole max (and it is also indicated by the model number), I count 26
"your home inspector shoulda seen that, hon."
View Profile
Lafayette, Louisiana
Posts: 3859
Joined: Nov, 2009
Currently offline offline
  
Overfull panel
[#12] Posted: 04/15/2012 - 4:03:47 PM
Reply with Quote
Quote: Originally posted by Jim Katen

Quote: Originally posted by Inspectorjoe

"20 poles maximum" is printed on the label. It's too bad all panelboards don't contain that info.


I'd like to see the transform that produces 20 poles of power.

Why didn't they just say "20 breakers maximum."


Because some breakers might be 2 pole breakers that take up the space of 2 poles.

I call a 2 pole breaker a 'breaker', not 2 breakers.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
View Profile
Gaston, Oregon
Posts: 8092
Joined: Dec, 2003
Currently offline offline
  
Overfull panel
[#13] Posted: 04/15/2012 - 6:58:30 PM
Reply with Quote
Quote: Originally posted by Richard Moore

Quote: Originally posted by Jim Katen



Why didn't they just say "20 breakers maximum."

Well, then you would have some arguing that the 240 vac breaker for the range is just a single breaker. Johnny Homeowner buys and installs a "single" breaker, no matter how many poles it might have. The number of poles may still be a bit confusing, but perhaps it will at least get Bubba to ask questions.


But the words "20 poles maximum" do not restrict what was done here. Each tandem breaker still has a single connection to a single pole. The installation in the pictures still has only 20 "poles" (to use their bizarre term for each position on the bus bar).

Jim Katen, Oregon
www.amipdx.com
View Profile
Gaston, Oregon
Posts: 8092
Joined: Dec, 2003
Currently offline offline
  
Overfull panel
[#14] Posted: 04/15/2012 - 7:00:58 PM
Reply with Quote
Quote: Originally posted by Marc

Quote: Originally posted by Jim Katen

Quote: Originally posted by Inspectorjoe

"20 poles maximum" is printed on the label. It's too bad all panelboards don't contain that info.


I'd like to see the transform that produces 20 poles of power.

Why didn't they just say "20 breakers maximum."


Because some breakers might be 2 pole breakers that take up the space of 2 poles.

I call a 2 pole breaker a 'breaker', not 2 breakers.

Marc


Then what do you call two breakers that take up a single pole?


The terminology is both wrong (because these panels only have two "poles") and confusing.

Jim Katen, Oregon
www.amipdx.com
View Profile
Lafayette, Louisiana
Posts: 3859
Joined: Nov, 2009
Currently offline offline
  
Overfull panel
[#15] Posted: 04/15/2012 - 7:27:55 PM
Reply with Quote
Quote: Originally posted by Jim Katen

Quote: Originally posted by Marc

Quote: Originally posted by Jim Katen

Quote: Originally posted by Inspectorjoe

"20 poles maximum" is printed on the label. It's too bad all panelboards don't contain that info.


I'd like to see the transform that produces 20 poles of power.

Why didn't they just say "20 breakers maximum."


Because some breakers might be 2 pole breakers that take up the space of 2 poles.

I call a 2 pole breaker a 'breaker', not 2 breakers.

Marc


Then what do you call two breakers that take up a single pole?


The terminology is both wrong (because these panels only have two "poles") and confusing.


Duplex breaker.

I agree there is a problem with the terminology. Don't newer panels specify 'maximum circuits' instead of 'maximum poles'?

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
Chico, CA
Posts: 21
Joined: Dec, 2009
Currently offline offline
  
Overfull panel
[#16] Posted: 04/15/2012 - 10:57:44 PM
Reply with Quote
The twin breakers installed in the GE, Goverment Electric panel are not GE, & I doubt they are UL classified to be used in one. GE twin breakers are peculiar to GE & they will not fit a non-GE manufactured panel.
View Profile
Gaston, Oregon
Posts: 8092
Joined: Dec, 2003
Currently offline offline
  
Overfull panel
[#17] Posted: 04/16/2012 - 12:03:06 AM
Reply with Quote
Quote: Originally posted by Norcal

The twin breakers installed in the GE, Goverment Electric panel are not GE, & I doubt they are UL classified to be used in one. GE twin breakers are peculiar to GE & they will not fit a non-GE manufactured panel.


Good point. Those are Siemen's breakers - almost certainly not classified for use with GE.

Jim Katen, Oregon
www.amipdx.com
Chestertown, MD
Posts: 214
Joined: Apr, 2009
Currently offline offline
  
Overfull panel
[#18] Posted: 04/16/2012 - 7:40:56 PM
Reply with Quote
A 2 pole breaker counts as two poles, however if you were to count circuits it would be one.
   
Previous Topic: Doube Taps - Topic - Next Topic: GECs On EGC Bars - Not Service Neutral Bar New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000