[#1] Posted: 05/01/2012 - 7:39:28 PM
Reply with Quote
Today' inspection had an old 100 amp Bulldog Pushmatic panel that I have a couple of questions about.

At the top of the panel they tapped off the main lugs for a 60 amp breaker for an A/C and there was one other wire that went to a old fuse for a furnace. This is wrong, right? You don't tap off the main lugs, right.


Click to View

53.6 KB


Click to View

52.18 KB

There was also a subpanel that was fed off of the 2 copper lugs at the bottom of the panel, but there was no main disconnect in the subpanel. Is this right? Does that make this a 100 amp subpanel?



Click to View

54.06 KB


Click to View

47.55 KB
I got the ground on the neutral bus in the sub covered already.

Thanks for your help,
Jim

View Profile
Victoria, British Columbia
Posts: 2396
Joined: Nov, 2009
Currently offline offline
  
Bulldog Pushmatic panel questions
[#2] Posted: 05/01/2012 - 8:59:42 PM
Reply with Quote
I'm not an expert, but I know the small conductor tap at the top for the fuse panel is wrong.
There is a tap rule in the NEC which I can't quote, but the AC might not be a violation. But those lugs need to be rated for more than one conductor.

I believe the taps at the bottom for the subpanel are undersized. They need to be sized to handle the full supply, which you say is 100 amps. Or they should be protected by a breaker in the main panel. It is amateur work, no doubt.

Is there a 100 amp disconnect out by the meter?

www.allsafehome.ca
View Profile
Gaston, Oregon
Posts: 8083
Joined: Dec, 2003
Currently offline offline
  
Bulldog Pushmatic panel questions
[#3] Posted: 05/01/2012 - 9:29:38 PM
Reply with Quote
Quote: Originally posted by In-Depth

Today' inspection had an old 100 amp Bulldog Pushmatic panel that I have a couple of questions about.

At the top of the panel they tapped off the main lugs for a 60 amp breaker for an A/C and there was one other wire that went to a old fuse for a furnace. This is wrong, right? You don't tap off the main lugs, right.

Yes, you're right. The taps are not correct.

Quote: There was also a subpanel that was fed off of the 2 copper lugs at the bottom of the panel, but there was no main disconnect in the subpanel. Is this right? Does that make this a 100 amp subpanel?

It makes it an unprotected panel. I suppose that it's capacity is limited by the size of the feeders -- what, #8 or so? -- not nearly big enough for 100 amps. They need to either feed it through a breaker, install a backfed main in the sub panel, or replace it with a main breaker panel.

Jim Katen, Oregon
www.amipdx.com
View Profile
Atlanta, ga
Posts: 120
Joined: Apr, 2009
Currently offline offline
  
Bulldog Pushmatic panel questions
[#4] Posted: 05/09/2012 - 10:32:56 AM
Reply with Quote
It is improper because it does not protect people and equipment.
#1) The wire is not protected and can overheat because the breaker protecting it will allow a higher than rated current - causing overheating and failure.
#2) The equipment requires a breaker of a certain size to protect it from pulling a load higher than designed - which could also cause overheating, arcing, and failure of the equipment.
#3) I *believe* that the lug is only rated for one wire. ditto for safety. overheating leading to breakdown of insulation and wiring leading to arcing and yada yada yada....

Chico, CA
Posts: 21
Joined: Dec, 2009
Currently offline offline
  
Bulldog Pushmatic panel questions
[#5] Posted: 05/29/2012 - 06:44:12 AM
Reply with Quote
If you look at the 2nd pic, there are 2 100A mains, 1 for each row. The taps off the main lugs is not kosher, remember there is NO overcurrent protection there.
windber, pa
Posts: 3
Joined: Jun, 2012
Currently offline offline
  
Bulldog Pushmatic panel questions
[#6] Posted: 06/19/2012 - 5:31:08 PM
Reply with Quote
this panel is not a main panel it should have a disconnect switch before the main wires enter this panel. this is a main lug panel.besides in PA we do not accept pushmatic anymore
View Profile
State: PA & NJ
Posts: 3208
Joined: Jan, 2004
Currently offline offline
  
Bulldog Pushmatic panel questions
[#7] Posted: 06/19/2012 - 8:10:04 PM
Reply with Quote
Quote: Originally posted by mikewi

this panel is not a main panel it should have a disconnect switch before the main wires enter this panel. this is a main lug panel.besides in PA we do not accept pushmatic anymore
Who is "we" in PA?

Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources
   
Previous Topic: 24V DC lighting - Topic - Next Topic: wadsworth panels New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000