attic sheathing
[#2] Posted: 06/22/2012 - 6:36:56 PM |  | |
|
There's a few options to the FRT. They could have installed firesheet on the underside of the rafters for a distance of 4' from the firewall. Another is to extend the firewall above the roof deck.
Without any of those, the firewall loses it's rating.
Marc
|
"If Guam gets too overpopulated, it might tip over." Congressman Hank Johnson (D) GA |
| |
|
|
| |
 |
Reisterstown, Maryland Posts: 265
Joined: Apr, 2011
| online |
|
|
|
| |
 |
Chicago, IL Posts: 9502
Joined: Dec, 2003
| offline |
|
attic sheathing
[#4] Posted: 06/22/2012 - 7:39:11 PM |  | |
|
That's my guess. Bad bunch of FRT plywood.
|
Kurt in Chicago
"If I smell it, it goes in the report".............Phillip Smith...2012
|
| |
|
|
| |
 |
Severna Park, Maryland Posts: 3458
Joined: May, 2007
| offline |
|
attic sheathing
[#5] Posted: 06/22/2012 - 8:09:03 PM |  | |
|
Thanks for the input and I'm aware of the possible issues with FRT. It's not that it was replaced that I'm questioning. I'm questioning the OSB (not fire rated) butting up to the firewalls at the adjoining units.
On another angle, considering all the sheathing was replaced, that constitutes structural work, correct? Therefore, would a permit be required normally?
|
John Dirks Jr - Arundel Home Inspection LLC - MD license: 29827 Maryland Home Inspectors - Maryland Home Inspection - Maryland Radon Testing - Baltimore County Rental Inspection
|
| |
|
|
| |
 |
Severna Park, Maryland Posts: 3458
Joined: May, 2007
| offline |
|
|
|
| |
 |
Severna Park, Maryland Posts: 3458
Joined: May, 2007
| offline |
|
|
|
| |
 |
State: PA & NJ Posts: 3208
Joined: Jan, 2004
| offline |
|
attic sheathing
[#8] Posted: 06/22/2012 - 8:39:52 PM |  | |
|
706.6 Vertical continuity. Fire walls shall extend from the foundation to a termination point at least 30 inches (762 mm) above both adjacent roofs.
Exceptions:
1. Stepped buildings in accordance with Section 706.6.1 (see below). 2. Two-hour fire-resistance-rated walls shall be permitted to terminate at the underside of the roof sheathing, deck or slab, provided: 2.1. The lower roof assembly within 4 feet (1220 mm) of the wall has not less than a 1-hour fire-resistance rating and the entire length and span of supporting elements for the rated roof assembly has a fire-resistance rating of not less than 1 hour. 2.2. Openings in the roof shall not be located within 4 feet (1220 mm) of the fire wall. 2.3. Each building shall be provided with not less than a Class B roof covering. 3. Walls shall be permitted to terminate at the underside of noncombustible roof sheathing, deck or slabs where both buildings are provided with not less than a Class B roof covering. Openings in the roof shall not be located within 4 feet (1220 mm) of the fire wall. 4. In buildings of Type III, IV and V construction, walls shall be permitted to terminate at the underside of combustible roof sheathing or decks, provided: 4.1. There are no openings in the roof within 4 feet (1220 mm) of the fire wall, 4.2. The roof is covered with a minimum Class B roof covering, and 4.3. The roof sheathing or deck is constructed of fire-retardant-treated wood for a distance of 4 feet (1220 mm) on both sides of the wall or the roof is protected with 5/8-inch (15.9 mm) Type X gypsum board directly beneath the underside of the roof sheathing or deck, supported by a minimum of 2-inch (51 mm) nominal ledgers attached to the sides of the roof framing members for a minimum distance of 4 feet (1220 mm) on both sides of the fire wall. 5. In buildings designed in accordance with Section 509.2, fire walls located above the 3-hour horizontal assembly required by Section 509.2, Item 1 shall be permitted to extend from the top of this horizontal assembly. _____________________________________________________ 706.6.1 Stepped buildings. Where a fire wall serves as an exterior wall for a building and separates buildings having different roof levels, such wall shall terminate at a point not less than 30 inches (762 mm) above the lower roof level, provided the exterior wall for a height of 15 feet (4572 mm) above the lower roof is not less than 1-hour fire-resistance-rated construction from both sides with openings protected by fire assemblies having a fire protection rating of not less than 3/4 hour.
Exception: Where the fire wall terminates at the underside of the roof sheathing, deck or slab of the lower roof, provided: 1. The lower roof assembly within 10 feet (3048 mm) of the wall has not less than a 1-hour fire-resistance rating and the entire length and span of supporting elements for the rated roof assembly has a fire-resistance rating of not less than 1 hour. 2. Openings in the lower roof shall not be located within 10 feet (3048 mm) of the fire wall.
|
| Bill Kibbel, Historic & Commercial Building Inspections - Old House Resources |
| |
|
|
| |
 |
Severna Park, Maryland Posts: 3458
Joined: May, 2007
| offline |
|
|
|
| |
 |
Garland, Texas Posts: 201
Joined: Mar, 2002
| offline |
|
attic sheathing
[#10] Posted: 06/22/2012 - 10:51:30 PM |  | |
|
the pic doesn't appear to be a "firewall" assembly?
as i understand gypsum board firewall assembly: all gaps and penetrations must be filled with taping compound, fireproof sealant or stuffed with non-combustible material
i've slung more 5/8 type x and mud than i care to admit
|
Barry Adair trec#4563 http://www.adairinspection.com life is the random lottery of events followed by numerous narrow escapes...accept the good |
| |
|
|
| |
 |
State: PA & NJ Posts: 3208
Joined: Jan, 2004
| offline |
|
|
|
| |
 |
Severna Park, Maryland Posts: 3458
Joined: May, 2007
| offline |
|
attic sheathing
[#12] Posted: 06/23/2012 - 05:48:46 AM |  | |
|
Quote: Originally posted by Bill KibbelQuote: Originally posted by John Dirks Jr
Bill, 706 is on track but I think the one you posted is from 2009. Unfortunately, the local jurisdiction in question is still in 2003 IRC. I'm digging there now. The '03 version if a bit different on the topic.
For 2003, see R317.2.2 Parapets. "Exception: A parapet is not required in the two cases above when the roof is covered with a minimum class C roof covering, and the roof decking or sheathing is of noncombustible materials or approved fire-retardant-treated wood for a distance of 4 feet on each side of the wall or walls, or one layer of 5/8-inch Type X gypsum board is installed directly beneath the roof decking or sheathing for a distance of 4 feet on each side of the wall or walls".
Thanks Bill. As a matter of fact I found that one last night and wanted to respond but the forum went down.
http://publicecodes.citation.c...r004.htm
I'll be checking with the AHJ to get their take on the situation too. I'll let you know what they say.
I'm thinking the entire sheathing change might have required a permit as well and there are no permits on file for that work at that property. Now, even though it was built in '85, if permit required work was done in 2012, wouldn't that mean that adhering to the current adopted code would be required? IE 2003 IRC R317.2.2 Parapets.
|
John Dirks Jr - Arundel Home Inspection LLC - MD license: 29827 Maryland Home Inspectors - Maryland Home Inspection - Maryland Radon Testing - Baltimore County Rental Inspection
|
| |
|
|
| |
 |
Severna Park, Maryland Posts: 3458
Joined: May, 2007
| offline |
|
|
|
| |
 |
Garland, Texas Posts: 201
Joined: Mar, 2002
| offline |
|
attic sheathing
[#14] Posted: 06/23/2012 - 07:48:04 AM |  | |
|
Quote: Originally posted by John Dirks JrQuote: Originally posted by BADAIR
the pic doesn't appear to be a "firewall" assembly?
as i understand gypsum board firewall assembly: all gaps and penetrations must be filled with taping compound, fireproof sealant or stuffed with non-combustible material
i've slung more 5/8 type x and mud than i care to admit
It appeared to be double layered gypsum with staggered joints. I saw gaps with another layer underneath. Would that make a difference as to the requirement of taped joints?
material, fastener spacing, sealing all seams and gaps is/was required on every gypsum board firewall assembly (gbfwa) i've ever seen or built
a fire marshal explained, "stopping air passage, stops flame spread" simple physics
imo & documented, it's not a tried & true UL tested gbfwa without these details, just unit/space separation in that case
this may assist http://www.usg.com/rc/system-c...A100.pdf
aside: the backside visible would also be a deal killer for this as a gbfwa different paper has not met or would not meet the test requirements
any ahj that would pass that as a gbfwa doesn't care or understand the potential ramifications
|
Barry Adair trec#4563 http://www.adairinspection.com life is the random lottery of events followed by numerous narrow escapes...accept the good |
| |
|
|
| |
 |
Denver, CO Posts: 307
Joined: Dec, 2005
| offline |
|
attic sheathing
[#15] Posted: 06/25/2012 - 10:56:09 PM |  | |
|
And just in case anyone isn't clear on the potential ramifications...
Here's a photo I took recently while on vacation, showing what's left of a 4-unit townhome.
Click to View
 97.87 KB
|
Garet Denise www.Cornerstone-Inspection.com
Our knowledge of wisdom exceeds our wise use of knowledge. |
| |
|
|
| |
 |
Reisterstown, Maryland Posts: 265
Joined: Apr, 2011
| online |
|
attic sheathing
[#16] Posted: 06/26/2012 - 06:33:00 AM |  | |
|
Quote: Here's a photo I took recently while on vacation, showing what's left of a 4-unit townhome. Click to View
97.87?KB
I may be wrong, but it seems to me the purpose of the code is to allow sufficient time for evacuation, not to save the structure.
A long FD response time (remote, inaccessible location), lack of water, weather, prevailing wind, etc. Ultimately fire will take everything, code or no code.
|
Bob Kenney www.IndependentHomeInspectionMD.com "We are masters of the unspoken word, and slaves to those we speak." Winston Churchill |
| |
|
|
| |
 |
Denver, CO Posts: 307
Joined: Dec, 2005
| offline |
|
attic sheathing
[#17] Posted: 06/26/2012 - 1:32:34 PM |  | |
|
The photo is from the middle of Vail, Colorado. I doubt that fire department response time or resources were a factor. Obviously, it was a major fire (it even spread to the next building over) and when Mother Nature goes on a rampage it's best to keep your distance. But the point is that fire spreading from one living unit to the next is a very real concern with devastating consequences.
|
Garet Denise www.Cornerstone-Inspection.com
Our knowledge of wisdom exceeds our wise use of knowledge. |
| |
|
| |
|
|