Generator sub panel

Previous Topic: Two circuits - Single neutral & GFCI - Topic - Next Topic: 24V DC lighting New TopicReply to TopicShare Topic
Posted By  
View Profile
Linden, MI
Posts: 225
Joined: Feb, 2004
Currently offline offline
  
Thread Start First Page
[#1] Posted: 06/25/2012 - 07:17:30 AM
Reply with Quote

I inspected a sub panel that contained only the circuits that were being back fed from a generator. The only wiresw that terminated in this sub panel were the hot conductors. The grounds and neutrals remained in the main panel. Is this the correct way to do it?

I called it out as a problem and now they have a sparky telling me that I am wrong. That's fine, I have been wrong before.

The only thing I can find to support my opinion is:
E3306.7, which basically says all conductors of the circuit needs to be in the same raceway, cable, or cord. That may be what was stuck in my head why all wires should terminate in the same panel.

I have no problem telling the customer that I was wrong but I don't want to just take the sparkies word for it. Of course no permits were pulled from this subpanel.



Mark Mustola
ValueCheck Home Inspections
Linden, MI
www.ValueCheckInspections.com
View Profile
Lafayette, Louisiana
Posts: 3846
Joined: Nov, 2009
Currently offline offline
  
Generator sub panel
[#2] Posted: 06/25/2012 - 07:45:52 AM
Reply with Quote
If your description is accurate, that sparky is a twit. Stand your ground.

The intent of E3306.6 is to provide for the cancellation of magnetic fields generated by the alternating current, otherwise small scale inductive heating of nearby conductive materials can result.

Marc

"If Guam gets too overpopulated, it might tip over."
Congressman Hank Johnson (D) GA
Posts: 662
Joined: Feb, 2004
Currently offline offline
  
Generator sub panel
[#3] Posted: 06/25/2012 - 2:16:13 PM
Reply with Quote
Check out this page and download the pdf for the installation directions. It shows one green and one white from the transfer switch to the main panel from the generator switch.
http://reliancecontrols.com/Pr...x?20216A

View Profile
Victoria, British Columbia
Posts: 2390
Joined: Nov, 2009
Currently offline offline
  
Generator sub panel
[#4] Posted: 06/25/2012 - 3:56:26 PM
Reply with Quote
There needs to be a proper transfer switch which cuts power from the main service before the generator is switched in. If that switch is installed correctly, then there will be a 4-wire cable joining the two panels. If not, then it is WRONG.
www.allsafehome.ca
View Profile
Linden, MI
Posts: 225
Joined: Feb, 2004
Currently offline offline
  
Generator sub panel
[#5] Posted: 06/25/2012 - 7:13:42 PM
Reply with Quote

There is a transfer switch of sorts. There are two double breakers connected by an pivoting lever. one breaker is fed with power from the generator and the other is fed from the main panel. So to circuits that are powered by this sub panel can only be powered by the power company or the generator not both at the same time.

I have never seen a set up like this before.

Mark Mustola
ValueCheck Home Inspections
Linden, MI
www.ValueCheckInspections.com
View Profile
Collins, NY
Posts: 3138
Joined: Apr, 2008
Currently offline offline
  
Generator sub panel
[#6] Posted: 06/26/2012 - 06:25:29 AM
Reply with Quote
I found one of these a few months ago. The thread is here http://www.inspectorsjournal.c...r,switch

I actually prefer this arrangement, every other transfer switch I run across has far too many pigtails jammed into an already overstuffed 100 amp enclosure.

Tom

http://clearcreekhomeinspection.com/

Life is tough enough as it is, it's tougher when your stupid. Don't do stupid things.
Dr Joe Lstiburek
View Profile
Jefferson Twp., NJ
Posts: 417
Joined: Apr, 2005
Currently offline offline
  
Generator sub panel
[#7] Posted: 06/26/2012 - 4:20:10 PM
Reply with Quote
Quote: Originally posted by ghentjr

Check out this page and download the pdf for the installation directions. It shows one green and one white from the transfer switch to the main panel from the generator switch.
http://reliancecontrols.com/Pr...x?20216A


Dedicated transfer switch panels like this are different than a sub panel rigged for a generator.
If it is a sub panel, then as Marc said, electrical code requires all circuit wire routed together. I also agree with the Twit assessment. Likely the sparky saying there is nothing wrong with it is the same one that installed it that way.



Kyle Kubs
Benchmark Home Inspection Services
New Jersey NJ
   
Previous Topic: Two circuits - Single neutral & GFCI - Topic - Next Topic: 24V DC lighting New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000