[#1] Posted: 05/17/2007 - 2:40:03 PM
Reply with Quote
Long time since I posted here. But I have a question. I ran into a metal roof today that was installed with the fasteners in the valley of the corrugated sheets. I am under the impression that the fasteners should be installed on the ridges and not the valleys. Am I mistaken?

Peoria, Arizona
Posts: 131
Joined: Feb, 2004
Currently offline offline
  
Metal roof fasteners
[#2] Posted: 05/17/2007 - 3:31:29 PM
Reply with Quote
I think it depends on if they are primary fasteners or secondary fasteners. I believe primary fasteners can be in the valleys.

Here are some web sites that you can check:

http://www.mtlsales.com/Technical/

http://www.metalroofing.org/

http://www.mcrma.co.uk/pdf/mcrma_t10.pdf

Jeff Euriech
Peoria Arizona

View Profile
Gaston, Oregon
Posts: 8092
Joined: Dec, 2003
Currently offline offline
  
Metal roof fasteners
[#3] Posted: 05/17/2007 - 7:39:34 PM
Reply with Quote
Quote: Originally posted by Kudzu

Long time since I posted here. But I have a question. I ran into a metal roof today that was installed with the fasteners in the valley of the corrugated sheets. I am under the impression that the fasteners should be installed on the ridges and not the valleys. Am I mistaken?


Some manufacturers specify installing the screws on the flat part of the metal. Some specify installing them on the ribs. You'd have to find the installation instructions for the particular product that you were looking at.

In my experience, the skill of the installer is way, way, way more important than the location of the screws.

- Jim Katen, Oregon

Jim Katen, Oregon
www.amipdx.com
View Profile
Rochester, New York
Posts: 4115
Joined: Dec, 2003
Currently offline offline
  
Metal roof fasteners
[#4] Posted: 05/18/2007 - 05:11:14 AM
Reply with Quote
Most of the metal buildings and roofs around here are now being installed by fastening in the flats. The screws should have a captive washer (in a cup) when used on roofs.
Chad Fabry
StructureSmart Home Inspection Rochester, NY
www.structuresmart.com
View Profile
Chicago, IL
Posts: 9508
Joined: Dec, 2003
Currently offline offline
  
Metal roof fasteners
[#5] Posted: 05/18/2007 - 08:09:10 AM
Reply with Quote
Almost always flats. If you run the fasteners in the ridges, they move back & forth when the panels expand & contract. Eventually, the washer opens up a gap & leaks. In the flats, they don't move back & forth nearly as much, and the washer can maintain it's seal better.

Like Katen said, depends on mfg., but it's almost always flats nowadays.

Kurt in Chicago

"If I smell it, it goes in the report".............Phillip Smith...2012


   
Previous Topic: Composition Shingles Over Wood Shingles - Topic - Next Topic: Mod Bit? New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000