Gaps between rafter and ridge board/ beam

Previous Topic: Garage Question - Topic - Next Topic: New Website for Permanent Wood Foundation Info New TopicReply to TopicShare Topic
Posted By  
View Profile
Newberg, OR
Posts: 2787
Joined: Mar, 2007
Currently offline offline
  
Thread Start First Page
[#1] Posted: 06/26/2007 - 12:39:03 PM
Reply with Quote
What is an allowable gap between the roof rafters and ridge board or ridge beams (both in my case)? I know that ideally there should be no gaps, but is there any leeway.
The house I inspected today was framed in the winter (corrosion on attic framing nails and stains on sheathing), and it appears that the rafters likely shrunk away from the ridge board once dry. There were numerous rafters that had up to half inch gaps with just framing nails securing the rafters to the ridge boards with no wood bearing.

I wrote this up on a property last week and the builder got furious and said that it was within allowable standards. I told him to provide a written standard that allowed the gaps... have not heard back.

If half inch gaps are excessive- what is an ideal repair- sistering, hangers?

Thanks



View Profile
Columbus, Mississippi
Posts: 3169
Joined: Dec, 2003
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#2] Posted: 06/26/2007 - 1:50:58 PM
Reply with Quote
I ran into that same thing a couple of weeks ago, with gaps ranging from 1/8 - 3/4 of an inch (of those that had gaps; not all did). I recommended fixing everything 1/4 inch and up by sistering on pieces at least 2 - 3 feet long (well secured), and ignoring the rest. I don't have a standard for that, just my experience in carpentry.

Once you get everything up and decked it's unlikely anything bad is ever going to happen, but come on; anything over 1/4 inch is a pretty good miss. I believe the builder's association has standards for that kind of thing, but they stink.

The first contractor they called wanted to tear the whole roof off and do it over. Get real. It ain't THAT bad.

Brian G.
That's A Bad Scratch....We'll Have to Take the Arm Off at the Shoulder

www.accuspecllc.com
View Profile
Rochester, New York
Posts: 4128
Joined: Dec, 2003
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#3] Posted: 06/26/2007 - 5:46:08 PM
Reply with Quote
Quote: The house I inspected today was framed in the winter (corrosion on attic framing nails and stains on sheathing), and it appears that the rafters likely shrunk away from the ridge board once dry.



Just so you now... lumber shrinks almost imperceptibly along its length. The directional instability is across the trunk of the tree not along the trunk.

Sloppy framing is the problem. Wood's affinity to absorb and release moisture and Mother Nature have nothing to do with the condition.

Chad Fabry
StructureSmart Home Inspection Rochester, NY
www.structuresmart.com
View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#4] Posted: 06/26/2007 - 9:56:09 PM
Reply with Quote
Quote: Originally posted by Chad Fabry

Quote: The house I inspected today was framed in the winter (corrosion on attic framing nails and stains on sheathing), and it appears that the rafters likely shrunk away from the ridge board once dry.



Just so you now... lumber shrinks almost imperceptibly along its length. The directional instability is across the trunk of the tree not along the trunk.

Sloppy framing is the problem. Wood's affinity to absorb and release moisture and Mother Nature have nothing to do with the condition.

What I typically see is that, as the rafter shrinks, the pointy end of the plumb cut remains in contact with the ridge board but the bottom end moves away from the ridge board. The shrinkage across the width of the rafter effectively causes the plumb cut to become more acute.

- Jim Katen, Oregon

Jim Katen, Oregon
www.amipdx.com
View Profile
Newberg, OR
Posts: 2787
Joined: Mar, 2007
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#5] Posted: 06/26/2007 - 10:03:29 PM
Reply with Quote
Brian,
I am glad I am not the only one making this call-- I'm still hoping to find documentation somewhere to back it up.

View Profile
Columbus, Mississippi
Posts: 3169
Joined: Dec, 2003
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#6] Posted: 06/26/2007 - 10:08:45 PM
Reply with Quote
I think they must've had a cross-eyed guy on the crew the day they did the one I looked at. This wasn't shrinkage, the gaps were even up and down the plumb cut. Somebody just kept missing the measurement every other rafter or so, which they decided to hide at the ridge. Pitiful.

Brian G.
Job Security Forever

www.accuspecllc.com
View Profile
Newberg, OR
Posts: 2787
Joined: Mar, 2007
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#7] Posted: 06/26/2007 - 10:54:54 PM
Reply with Quote
This topic was discussed over at the ICC discussion site as well-
http://www.iccsafe.org/cgi-bin...t=001337

View Profile
Gaston, Oregon
Posts: 8139
Joined: Dec, 2003
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#8] Posted: 06/27/2007 - 12:53:34 AM
Reply with Quote
Quote: Originally posted by Brandon Whitmore

Brian,
I am glad I am not the only one making this call-- I'm still hoping to find documentation somewhere to back it up.


How about 802.6. The ends of each rafter or ceiling joist shall have not less than 1-1/2 inches of bearing on wood or metal and not less than 3 inches on masonry or concrete.

- Jim Katen, Oregon

Jim Katen, Oregon
www.amipdx.com
View Profile
Columbus, Mississippi
Posts: 3169
Joined: Dec, 2003
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#9] Posted: 06/27/2007 - 08:37:35 AM
Reply with Quote
Originally posted by Jim Katen

How about 802.6. The ends of each rafter or ceiling joist shall have not less than 1-1/2 inches of bearing on wood or metal and not less than 3 inches on masonry or concrete.

That's not bad. The ones I saw had zero bearing.

Brandon, I don't have time to dig around right now, but I'll bet if you could find some spec & tech stuff from nail manufacturers they make it clear their nails aren't designed to bear loads across big gaps between framing members. An email to one of those engineering departments might get you something.

Nobody argued with me when I called for repairs. I'd have trouble hiding my irritation if some jerk called me up to insist that 3/4 inch gaps in framing was fine. I see little misses all the time and I don't say anything, but jeez...learn to read a frickin' tape.

Brian G.
Okay Bob, Make It 188 and 7 of Those Little Marks


Image Insert:

9.42 KB

www.accuspecllc.com
View Profile
Kenmore, WA
Posts: 2101
Joined: Sep, 2004
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#10] Posted: 06/27/2007 - 09:43:35 AM
Reply with Quote
I've never looked myself but read a lot about the standards put out by N.A.H.B.- National Association of Home Builders.

Maybe their standards are online for free?

Randy Navarro
http://www.thecompleteinspection.com
View Profile
Newberg, OR
Posts: 2787
Joined: Mar, 2007
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#11] Posted: 06/27/2007 - 3:23:11 PM
Reply with Quote
Brian and Jim.

I will use the code referenced and also contact a nail manufacturer for a back up as well.

Brian-- they left your framing gap in that pic on purpose to allow for proper airflow at the ridge vent

Randy- thanks for the reference on the NAHB. I have their book and tried that prior to posting-- no such luck.

Thanks everyone.

View Profile
Georgetown, KY
Posts: 2209
Joined: Mar, 2002
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#12] Posted: 06/29/2007 - 11:32:08 AM
Reply with Quote
Just saw that this morning in a new home.



Image Insert:

40.51 KB

-


Erby Crofutt
B4U Close Home Inspections
Georgetown, KY
www.b4uclose.com
www.kentuckyhomeinspections.com
https://www.facebook.com/B4UCl...pections
Kentucky Home Inspections
Kentucky Home Inspectors
502-570-4054
View Profile
Lexington, KY
Posts: 2541
Joined: Nov, 2004
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#13] Posted: 06/29/2007 - 5:35:11 PM
Reply with Quote
Our state code requires roof framing to comply with the standards of the AFPA. When I catch flak from a builder, I have him check out their framing guide. There's a diagram and language that says the rafter end has to rest flush against the ridge board to avoid horizontal shear in the rafter.

If Mike will tell me how to zap a .pdf of the guide to him, he can post it in the library.

John

View Profile
Kenmore, WA
Posts: 15412
Joined: Dec, 2003
Currently online online
  
Gaps between rafter and ridge board/ beam
[#14] Posted: 06/29/2007 - 6:17:09 PM
Reply with Quote
That's easy,

Send it as an attachment to hausdok@inspectorsjournal.com ; or, if it's reachable through a url, just add it to the library yourself by posting the URL into the file directory under the appropriate category.

ONE TEAM - ONE FIGHT!!!

Mike

Taunton, MA
Posts: 28
Joined: Mar, 2007
Currently offline offline
  
Gaps between rafter and ridge board/ beam
[#15] Posted: 07/03/2007 - 05:36:44 AM
Reply with Quote
Erby,

What would you report about the splice in the ridge board? It may be acting as a mechanical connection between the opposing rafters, but it will also be transferring some load to it's endbearing - right?. Not to mention the less than ideal placement of the splice.

   
Previous Topic: Garage Question - Topic - Next Topic: New Website for Permanent Wood Foundation Info New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000