[#1] Posted: 09/08/2007 - 10:55:30 PM
Reply with Quote
In an old house with an unlined 7.5 x11.5 chimney, I need to know what is the proper metal flue liner size to use. There is an old gas furnace with a 4 " vent and old water heater with a 3 " vent. They both use the flue. Some contractors are saying that there must be two liners, one for each device. Another, says that one larger flue is enough. Does any one know what the normal code is?

View Profile
Kenmore, WA
Posts: 15722
Joined: Dec, 2003
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#2] Posted: 09/09/2007 - 01:47:12 AM
Reply with Quote
Why would you even want to screw around with this or get into the middle of something between a couple of HVAC contractors? Once it's referred off to an HVAC guy, let him tell them what they need, and if they call you up wanting your opinion of it just tell them that you're the family doctor and he's the brain surgeon; it's his call, not your's to make.

If you must know, you can use one flue but it needs to be equal to the area of the largest vent plus 1/2 of all others.

A 4 inch vent has 12.56 square inches.

A 3 inch vent has 7.065 square inches.

7.06/2 = 3.03 square inches

12.56 + 3.03 = 15.59 square inches.

A 5" vent has 19.62 square inches, so it should work fine, if it's ok to use a 3 inch vent on the water heater and a 4 inch vent on the furnace. Do you know that it is?

Unless you have years of HVAC work and experience specifying HVAC systems under your belt, it's really not very smart to get involved with specifying stuff like this - especially when it involves venting "old" gas appliances into a cold chimney stack. If you do that and either of them backdrafts into the home and sickens or kills someone, you could end up losing everything.

OT - OF!!!

M.


Richmond, Virginia
Posts: 7
Joined: Aug, 2006
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#3] Posted: 09/09/2007 - 05:43:40 AM
Reply with Quote
Dear Mr hausdok,

Thank you for your quick response. The reason why I am interested in this is because I own the house and will be needing to do this work, and want a safe environment.

The one contractor that said I needed two flue liners had a price that was about twice as high as the one that was going to install only one liner. And he said that it was the code to have a separate flue liner for each appliance.

View Profile
Gervais, Oregon
Posts: 1260
Joined: Jul, 2006
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#4] Posted: 09/09/2007 - 07:25:19 AM
Reply with Quote
If the natual draft gas appliances are not on the same floor and taking combustion air from the same space, wouldn't they require separate vents?

Chris, Oregon

View Profile
Ridgewood, NJ
Posts: 1010
Joined: Sep, 2002
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#5] Posted: 09/09/2007 - 08:38:30 AM
Reply with Quote
If both of the appliances are old, how about replacing them with direct vent, more efficient, units. You'll save the cost of relining the chimney.
Neal Lewis
www.totalhomeinspectionservices.com
Champaign, Illinois
Posts: 515
Joined: Sep, 2006
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#6] Posted: 09/09/2007 - 09:53:24 AM
Reply with Quote
Quote: Originally posted by Neal Lewis

If both of the appliances are old, how about replacing them with direct vent, more efficient, units. You'll save the cost of relining the chimney.



Plus get the federal tax deduction, before Dec 31, 2007.

Richmond, Virginia
Posts: 7
Joined: Aug, 2006
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#7] Posted: 09/09/2007 - 11:27:41 AM
Reply with Quote
Both the water heater and furnace are in the basement venting into the same flue. I am selling the house some replacing the them is not an option.
Nashville, TN
Posts: 1375
Joined: May, 2007
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#8] Posted: 09/09/2007 - 1:24:39 PM
Reply with Quote
Quote: Originally posted by Southbeach

Both the water heater and furnace are in the basement venting into the same flue. I am selling the house some replacing the them is not an option.


Sell the house "as is," and let the buyers worry about it. Or, get an estimate from a decent chimney guy, and give the amount of the estimate to the buyers as a credit.

Maybe it's just me, but if I'm selling a house, the last thing I want is the job of overseeing repairs. If something goes wrong, the buyer will want me to take care of it; and, he'd complain that I should've known about and disclosed this or that...

WJ

View Profile
Gaston, Oregon
Posts: 8837
Joined: Dec, 2003
Currently offline offline
  
Correct flue liner size? Or two flue liners neede?
[#9] Posted: 09/10/2007 - 12:41:12 AM
Reply with Quote
Quote: Originally posted by Southbeach

In an old house with an unlined 7.5 x11.5 chimney, I need to know what is the proper metal flue liner size to use. There is an old gas furnace with a 4 " vent and old water heater with a 3 " vent. They both use the flue. Some contractors are saying that there must be two liners, one for each device. Another, says that one larger flue is enough. Does any one know what the normal code is?

One flue is fine.
Two flues are better.
In my house, I used one flue. No complaints.

- Jim Katen, Oregon


Jim Katen, Oregon
www.amipdx.com
   
Previous Topic: flashing - Topic - Next Topic: Why bother New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000