Bath exhaust duct venting requirements

Previous Topic: Trane furnace age - Topic - Next Topic: Mixed radiators and hybrid gravity warm air New TopicReply to TopicShare Topic
Posted By  
View Profile
Newberg, OR
Posts: 2866
Joined: Mar, 2007
Currently offline offline
  
Thread Start First Page
[#1] Posted: 07/18/2011 - 10:28:52 PM
Reply with Quote
I am away from my office / book right now, but am being challenged on something I wrote up.
A bath exhaust fan was not vented to the exterior (no duct). I wrote if up and specified that they vent directly to the exterior. All they did was push up a duct near the roof vent opening; my re- inspect report indicated the need to vent DIRECTLY to the exterior. The HVAC guy send a retort saying that I am wrong and that it meets code. Do any of you have the code or commentary handy that I can send out to them tonight?

Here's what I have so far:
Air must be exhausted directly to the outside 2006 IRC [303.3X]
May not discharge to crawlspace or attic 2006 IRC [1501]


And from a couple of manufacturers instructions:
NuTone

Broan

I know that many/ most building officials are keying in on the word "directly", and making contractors do more than just push the ducts up near a roof vent, and have seen why many times. Does the commentary address this?(I hope)

TIA.

Brandon

Portland Home Inspector
View Profile
Dallas, TX
Posts: 1269
Joined: Oct, 2006
Currently offline offline
  
Bath exhaust duct venting requirements
[#2] Posted: 07/19/2011 - 04:58:01 AM
Reply with Quote
Brandon,

From the 2006 IRC Code/Commentary. The commentary says that pointing to an existing static vent cap or such is not acceptable.


===================

M1501.1 Outdoor discharge. The air removed by every
mechanical exhaust system shall be discharged to the outdoors.
Air shall not be exhausted into an attic, soffit, ridge vent or
crawl space.

Exception: Whole-house ventilation-type attic fans that
discharge into the attic space of dwelling units having private
attics shall be permitted.

The primary intent of this section is to avoid exhausting
contaminants into areas that may be occupied by people
or into concealed spaces such as attics and crawl
spaces where moisture can damage the building components.
To prevent the introduction of contaminants
into the ventilation air of a building, exhaust openings
must not direct exhaust so that it could be readily
drawn in by a ventilating system. In this situation, the
code official must determine an appropriate separation
or location for the placement of intake and exhaust
openings.
Attics and crawl spaces are not considered to be
outdoors. Exhaust ducts cannot terminate in these
spaces. Exhaust ducts must connect directly to terminals
that pass through the building envelope to the outside
atmosphere. Pointing, aiming or similarly directing
an exhaust pipe or duct at an opening in the
envelope of the building (that is, attic louver, grille,
ridge vent, eave vent or soffit vent) in no way ensures
that all or any of the exhaust will reach the outdoors. In
fact, it is possible that the majority, if not all, of the exhaust
vapors and gases will discharge to the attic
space rather than to the outdoors.


Cheers,

Nolan E. Kienitz
Nolan's Inspections, LLC
Dallas Home Inspections
http://www.NolansInspections.com
Olathe, KS
Posts: 268
Joined: Feb, 2004
Currently offline offline
  
Bath exhaust duct venting requirements
[#3] Posted: 07/19/2011 - 05:24:11 AM
Reply with Quote
FWIW, in my area on both sides of the state line 99.99% of new construction fans vent next to a ridge vent. At least in my area, I haven't seen any problems from it being done (not saying it's right, just haven't seen problems from it). I used to push to have people get them vented direct to the exterior on inspections, but have never seen any issues on 30+ year old houses without the extensions even ever being near the ridge vents (my own included). I now just recommend they extend them next to a ridge vent if the attic ventilation is done properly.
Kevin Wattenbarger
www.911owned.com
View Profile
Newberg, OR
Posts: 2866
Joined: Mar, 2007
Currently offline offline
  
Bath exhaust duct venting requirements
[#4] Posted: 07/19/2011 - 07:00:06 AM
Reply with Quote
Awesome-- thanks Nolan.

I was saying that placement of the ducts at/ near a vent didn't cause any problems a year or two back, and had a good debate over at IN. Since then, I've been paying close attention and have noticed some issues even when the duct is pushed right up to the screening. I'm not sure why, but there are times when the screening on the vents mold and plug up.


Brandon

Portland Home Inspector
View Profile
Dallas, TX
Posts: 1269
Joined: Oct, 2006
Currently offline offline
  
Bath exhaust duct venting requirements
[#5] Posted: 07/19/2011 - 12:51:46 PM
Reply with Quote
I think Erby has some quite descriptive images of what goes wrong when not vented properly.


Cheers,

Nolan E. Kienitz
Nolan's Inspections, LLC
Dallas Home Inspections
http://www.NolansInspections.com
View Profile
Newberg, OR
Posts: 2866
Joined: Mar, 2007
Currently offline offline
  
Bath exhaust duct venting requirements
[#6] Posted: 07/19/2011 - 1:35:07 PM
Reply with Quote
Thanks Nolan,

I have some pictures of my own somewhere, but not near as good as his.


First e- mail from listing agent:

Quote: The HVAC contractor will be sending me a note stating that his venting of the bath fan is done to current code. For the record, he came highly recommended to me years ago from XMI Home Inspectors, and he is a senior expert in his field, self-employed as such for 20+ years.


My reply was quite long and boring, so here was what I received via e- mail today



Quote: Buyer's Agent: "Read below - you win. Of course you did. I will need you to let me know if their itemized list of repairs for the siding will do the job, as it looks good to me.

Thanks again, you kick ass."



Quote: Listing Agent: "So, my assistant Katlin called Ron about faxing the cited code stuff to him, and apparently he had already called the city and learned that current code would in fact require a correction on his part, so he will be addressing that tomorrow at the property himself."



Thankfully, the code guy he spoke with knew what he was talking about, or this could have been drawn out, with or without all of the supporting documentation.







Brandon

Portland Home Inspector
View Profile
Victoria, British Columbia
Posts: 3168
Joined: Nov, 2009
Currently offline offline
  
Bath exhaust duct venting requirements
[#7] Posted: 07/19/2011 - 3:30:12 PM
Reply with Quote
In my climate, they not only need to be vented to the outside, but they also need to be sealed tight.
On the flip side, I've seen houses aplenty with plank sheathing and minimal attic insulation, where a loose bath vent hose has not caused any problem whatsoever.
Newer tight house with well insulated attic, no moist air is allowed.

Here's a couple of recent stains I had to talk about.
The first pic is directly above the master bath shower exhaust fan, short vent pipe straight up through the roof. Number two was a flaky duct tape seal.

Click to View

67.61 KB

Click to View

49.7 KB

www.allsafehome.ca
View Profile
indy, IN
Posts: 291
Joined: Jan, 2011
Currently offline offline
  
Bath exhaust duct venting requirements
[#8] Posted: 07/19/2011 - 7:10:46 PM
Reply with Quote
Quote: Originally posted by Brandon Whitmore

Thanks Nolan,

I have some pictures of my own somewhere, but not near as good as his.


First e- mail from listing agent:

Quote: The HVAC contractor will be sending me a note stating that his venting of the bath fan is done to current code. For the record, he came highly recommended to me years ago from XMI Home Inspectors, and he is a senior expert in his field, self-employed as such for 20+ years.


My reply was quite long and boring, so here was what I received via e- mail today



Quote: Buyer's Agent: "Read below - you win. Of course you did. I will need you to let me know if their itemized list of repairs for the siding will do the job, as it looks good to me.

Thanks again, you kick ass."



Quote: Listing Agent: "So, my assistant Katlin called Ron about faxing the cited code stuff to him, and apparently he had already called the city and learned that current code would in fact require a correction on his part, so he will be addressing that tomorrow at the property himself."



Thankfully, the code guy he spoke with knew what he was talking about, or this could have been drawn out, with or without all of the supporting documentation.









Go figure, a sub contractor trying to show up a home inspector by using code. Well maybe it was when he started 20+ years ago. "It was too hot to do it right"

Maybe you could add "kicks ass" to your buisness card. Nice complement.

View Profile
Gaston, Oregon
Posts: 8897
Joined: Dec, 2003
Currently offline offline
  
Bath exhaust duct venting requirements
[#9] Posted: 07/19/2011 - 9:38:16 PM
Reply with Quote
Quote: Originally posted by Brandon Whitmore

Thanks Nolan,

I have some pictures of my own somewhere, but not near as good as his.


First e- mail from listing agent:

Quote: The HVAC contractor will be sending me a note stating that his venting of the bath fan is done to current code. For the record, he came highly recommended to me years ago from XMI Home Inspectors, and he is a senior expert in his field, self-employed as such for 20+ years.

If XMI means AMI, please let me know who this guy is.

Quote: My reply was quite long and boring, so here was what I received via e- mail today



Quote: Buyer's Agent: "Read below - you win. Of course you did. I will need you to let me know if their itemized list of repairs for the siding will do the job, as it looks good to me.

Thanks again, you kick ass."



Quote: Listing Agent: "So, my assistant Katlin called Ron about faxing the cited code stuff to him, and apparently he had already called the city and learned that current code would in fact require a correction on his part, so he will be addressing that tomorrow at the property himself."



Thankfully, the code guy he spoke with knew what he was talking about, or this could have been drawn out, with or without all of the supporting documentation.


I like how they specified "current" code -- as if this has changed recently.

Jim Katen, Oregon
www.amipdx.com
View Profile
Newberg, OR
Posts: 2866
Joined: Mar, 2007
Currently offline offline
  
Bath exhaust duct venting requirements
[#10] Posted: 07/19/2011 - 11:29:15 PM
Reply with Quote
Jim,

PM being sent......

Brandon

Portland Home Inspector
View Profile
Sykesville, Maryland
Posts: 344
Joined: Nov, 2009
Currently offline offline
  
Bath exhaust duct venting requirements
[#11] Posted: 07/20/2011 - 03:34:22 AM
Reply with Quote
Good job, congrats on the kicking!
"This above all: to thine own self be true - -"
   
Previous Topic: Trane furnace age - Topic - Next Topic: Mixed radiators and hybrid gravity warm air New TopicReply to TopicShare Topic
Jump To:
The Inspector's Journal Forums © 2002-2013 all topics or replies that are posted on The Inspector's Journal
are copyrighted material of the original author that posted the topic or reply.
Go To Top Of Page 
 
Pick an RSS Feed

The views expressed on this website are the views of the authors and
do not necessarily reflect the views or policies of the sponsors.
© 2002-2013 Copyright DevWave Software Inc.
Find a Home Inspector

Powered By: Snitz Forums 2000