Water in the panel and outlets


Daniel Dodge

Recommended Posts

You can begin with NEC 110.12(C). 

Integrity of Electrical Equipment and Connections.
Internal parts of electrical equipment, including bus bars,
wiring terminals, insulators, and other surfaces, shall not be
damaged or contaminated by foreign materials such as paint,
plaster, cleaners, abrasives, or corrosive residues. There shall
be no damaged parts that may adversely affect safe operation
or mechanical strength of the equipment such as parts that
are broken; bent; cut; or deteriorated by corrosion, chemical
action, or overheating.

You might also want to study this document: 

http://www.nema.org/stds/water-damaged.cfm

(You'll have to create a NEMA user account, but it's not a big deal.) 

 

 

Link to comment
Share on other sites

19 hours ago, Daniel Dodge said:

Yes and if its necessary? 

Perfect Jim Thanks 

"There's water in the main breaker panel.  Rainwater is breaching the exterior wall or roof structure somewhere and getting into the panel.  It's a major issue because water and electricity do not play well together. Ask a carpenter or someone familiar with residential construction to find the leak and fix it.  Do this before the next rainfall."

Edited by Marc
Edited to make it better...and a little funny.
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...