Quick like a bunny. I'm having a senior moment and can't find the rule in the code that says a water heater vent connector to a common vent must enter higher than the connector from the furnace. Anyone know that one is lcoated off the top of your heads?

ONE TEAM - ONE FIGHT!!!

Mike

Share this post


Link to post
Share on other sites

NY mechanical code says:

803.7 Connectors serving two or more appliances. Where two or more connectors enter a common vent or chimney, the smaller connector shall enter at the highest level consistent with available headroom or clearance to combustible material.

Share this post


Link to post
Share on other sites

Was it this one?

From the 06' IRC

G2427.10.4 (503.10.4) Two or more appliances connected to a single vent. Where two or more vent connectors enter a common gas vent, chimney flue, or single-wall metal pipe, the smaller connector shall enter at the highest level consistent with the available headroom or clearance to combustible material.Vent connectors serving Category I appliances shall not be connected to any portion of a mechanical draft system operating under positive static pressure, such as those serving Category III or IV appliances.

Marc

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...