Heat Exchanger at 8 Years.


Bill Kibbel

Recommended Posts

Was this a horizontal mount?

That is, were the holes in a place where condensate could accumulate in the tubes?

No - upflow. There was clear evidence of a humidifier was likely located above the area of corrosion. Just one tube had a hole.

Bill,

How did you take the pictures, was there a vent on the plenum that allowed you to get your camera into and snap the shots?

This was a multiple building complex that took a few days. It was dismantled by an HVAC tech the day after I discovered a major problem with the flame entering the tube that had the hole. The other 3 burner flames didn't look right either. I suspected that a proper draft couldn't be induced if there was a large crack, hole or separation in one of the heat exchangers. I made a big stink about it and they called the company that installed it to come out and fix it.

The AC coil had been removed by the tech for a good look at the heat exchanger. The rest of the primary and the secondary still looked brand new. It seems that Nordyne might replace the exchanger assembly, but not pay for labor or shipping. I don't know that anyone mentioned to the manufacturer the possibility of a humidifier contributing to the failure.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...