Do you know (based on the NEC) if a sub-panel installed in 1978 required the seperation of the grounds and neutrals with the neutrals floating - like today?

Share this post


Link to post
Share on other sites

A lot would depend on whether this was in the same building or a detached structure and if there were other metallic paths like a phoe or water line run between the 2 buildings. More info is needed.

Share this post


Link to post
Share on other sites

All in same building.

In that case, the sub panel grounding conductors and neutral conductors were supposed to be isolated. Just like today. My reference is the 1975 NEC, Article 250-61(b).

I can personally only trace this back to the 1947 NEC.

Douglas has traced it back further, but I'm not sure about the edition. For some reason 1923 sticks in my head.

Jim Katen, Oregon

Share this post


Link to post
Share on other sites

All in same building.

In that case, the sub panel grounding conductors and neutral conductors were supposed to be isolated. Just like today. My reference is the 1975 NEC, Article 250-61(b).

I can personally only trace this back to the 1947 NEC.

Douglas has traced it back further, but I'm not sure about the edition. For some reason 1923 sticks in my head.

Jim Katen, Oregon

Other than GECs, would there be any grounding conductors before 1947?

Share this post


Link to post
Share on other sites

All in same building.

In that case, the sub panel grounding conductors and neutral conductors were supposed to be isolated. Just like today. My reference is the 1975 NEC, Article 250-61(b).

I can personally only trace this back to the 1947 NEC.

Douglas has traced it back further, but I'm not sure about the edition. For some reason 1923 sticks in my head.

Jim Katen, Oregon

Other than GECs, would there be any grounding conductors before 1947?

Yes. While there weren't equipment grounding conductors as we know them today, many of the old electrical books discuss grounding of conduits, cable sheaths, cabinets, frames, & so on.

Share this post


Link to post
Share on other sites

For awhile there, the conduits and boxes WERE the equipment grounding method. My 1964 home was built with grounded receptacles (3 prong) which relied on conduits for grounding.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...