I found a 220v double 15amp breaker in panel (15+15 = 30amp)

toggles factory fastened with metal clip.

top lug connected to red wire

bottom lug connected to black wire

single neutral and ground wire leaving panel with red and black

duplex outlet under kitchen sink

top of outlet connected to black wire and neutral white

ground connected

bottom of outlet connected to red wire and common ground, and seperate white.

bottom used for plug and cord to disposer

top used for plug and cord to dishwasher

no photos, new construction, muni inspected, the folks are not happy when I told them I have never seen this.

Anyone see this on a regular basis?

Share this post


Link to post
Share on other sites

The separate neutral thing is rather unnerving; are you sure it wasn't pigtailed?

Other than that, I see multiwire branch circuits serving the dishwasher and disposal all the time.

Share this post


Link to post
Share on other sites

Yeah,

Sounds like a 15-amp MWBC to me. Like Chad says, I bet that 'separate' white is pigtailed back in the box. See disposals and dishwashers on the same MWBC all the time.

ONE TEAM - ONE FIGHT!!!

Mike

Share this post


Link to post
Share on other sites

so the single throw will disconnect both? Wht is likely pigtailed. this is a condo sub panel, main is at meter three floors below.

Share this post


Link to post
Share on other sites

Up until recently, all Canadian counter outlets were wired that way - 15 amp split duplex*.

The tab on the hot side of the receptacle is snapped off to separate the top from the bottom. On the neutral side of the receptacle, the tab is left in place, so one neutral connection supplies top and bottom.

Les, since each leg supplies only one receptacle, you have two 120 volt, 15 amp supplies there. They are tied together to reduce the chance of a shock, safety issue for Sparky.

The new rules (CEC 2006) allow 20 amp so that people can have unsplit GFCI outlets around the sink.

Share this post


Link to post
Share on other sites

Thanks John, guess I knew that, but in this area we have not seen the breakers tied together at the panel

thanks guys!

Share this post


Link to post
Share on other sites
Thanks John, guess I knew that, but in this area we have not seen the breakers tied together at the panel

thanks guys!

Hasn't it been an NEC requirement for years? Of course, I don't know what code MI falls under.

Share this post


Link to post
Share on other sites

A double pole 15 is not a 30 amp breaker. It is a 15 amp breaker.

There should have been no reason to break the tab on the neutral side.

agreed!

Share this post


Link to post
Share on other sites

Thanks John, guess I knew that, but in this area we have not seen the breakers tied together at the panel

thanks guys!

That's because it wasn't required until the 2008 NEC. Before that, the breakers didn't need a tie bar. Without a tie bar, it wouldn't have shown up on your radar.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...