Is this Al wire ok in this breaker terminal?

It looks like it's too large. Is that a #6 conductor? The largest you can use is #8. If it's #8, you're supposed to put all of the strands under one side of the saddle, not split them up.

Do the markings on the breaker imply solid conductor wire only?

No. Solid or stranded is fine.

Link to comment
Share on other sites

Thank you so far.

The circuit is a 120v supply for the natural gas range. One can see the empty breaker below the top one in the pic--the original intention was to have a 240v electric range.

I couldn't i.d. the exact wire size. Anyone have good tricks for that if there's no visible marking on the cable?

Douglas--see you this weekend in Seattle at the ASHI WW seminar.

Jim--you going?

Anyone else going?

Link to comment
Share on other sites

Hadn't noticed when looking at this type of breaker before but it seems to indicate that you can only use one AL wire even though you can use two copper wires.

I believe that is correct - only one Al, and if you do attach two copper, the max wire gauge drops to #10.

Randy, I agree it is pretty hard to estimate wire size by just looking sometimes.

In this example, you would expect #8 Cu for a 40 amp range circuit. From that, I would deduce that Al to be a size larger - #6.

Link to comment
Share on other sites

What about incandescant lighting?

The SWD rating is an additional (and pretty meaningless) designation. It can also be used as a switch for other purposes, such as incandescent lighting.

I think the idea is that an older magnetic-ballast fluorescent has a greater initial current surge, and the SWD rating means that UL has evaluated it for a certain number of such operations without degradation of the internal contacts.

Link to comment
Share on other sites

Thank you so far.

The circuit is a 120v supply for the natural gas range. One can see the empty breaker below the top one in the pic--the original intention was to have a 240v electric range.

I couldn't i.d. the exact wire size. Anyone have good tricks for that if there's no visible marking on the cable?

Fetch yourself over to Ohm Depo and buy 2" lengths of each size of cable.

Douglas--see you this weekend in Seattle at the ASHI WW seminar.

Jim--you going?

Anyone else going?

I'm still trying to clear my schedule, but I'll try to be there.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...