John Dirks Jr Posted September 22, 2011 Report Share Posted September 22, 2011 Would you consider the yellow CSST sheathing a combustible material and therefore say it should not be so close to the water heater flue? Click to Enlarge 42.1 KB Link to comment Share on other sites More sharing options...
Marc Posted September 22, 2011 Report Share Posted September 22, 2011 This is all I could find. It's from the Gastite Installation Manual for CSST: LOCAL BUILDING CODES are controlling, however, as a general practice, fuel gas piping, including CSST, should not be installed within a chase or enclosure that houses a metallic chimney liner or appliance vent that protrudes through the roof. In the event such an installation is necessary and conforms to local building codes, the metallic chimney liner or vent must be bonded and grounded by a qualified electrical professional, and a separation distance, as specifically permitted by the applicable local building code between the CSST and the metallic chimney liner or vent, is required. Physical contact between CSST and the metallic chimney liner and/or vent is prohibited. If this physical separation cannot be specifically identified in the local building code and achieved or any local building code requirements cannot be met along the entire length, then rerouting of the CSST is required unless such installation is specifically permitted by the local building inspector. Marc Link to comment Share on other sites More sharing options...
Mike Lamb Posted September 22, 2011 Report Share Posted September 22, 2011 I would say it needs a 6" min. clearance from single walled gas appliance vent. I doubt the plastic coating is non-combustible. Link to comment Share on other sites More sharing options...
John Dirks Jr Posted September 22, 2011 Author Report Share Posted September 22, 2011 Although Marc showed that the CSST guide did not specifically prohibit the installation in question, I was thinking along the lines with Mike in that the polyester sheathing is combustible so therefore it must be at least 6" from the single wall vent of this gas appliance. Thanks for the discussion on the matter. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now