I'm looking for information on what would be a standard and approved method/material for fireblocking & draftstopping at the point the pipes for a high efficiency direct vent furnace enter the base of a wall chase on route to a through the roof install. Any information would be appreciated. This looks like it would be pain to install metal flashing around. Would ceramic wool be an option?

Thanks!

Click to Enlarge
tn_2013313154329_152%20-%20Copy.jpg

41.21 KB

Link to comment
Share on other sites

Wouldn't a fire rated expandable foam work. Great stuff and others make fire block spray.

Last time I looked at a can of that stuff, it specifically mentioned that it was intended to be used to fill small gaps, not large openings.

I see the orange foam often and never thought about fill limitations so I did some Googling.

From Dow on Great Stuff Fireblock:

Fills, seals and insulates gaps up to 1/2 inch

http://building.dow.com/na/en/products/ ... eblock.htm

According to the ICC which looks like it lumped all Great Stuff products into one:

A) Max. 1 5/16" wide, 3" thick max. B) max. 34 sq. in. per sq. ft.

http://www.icc-es.org/reports/pdf_files ... R-1961.pdf

Link to comment
Share on other sites

For single family homes, it's just not a big deal. Stuff the opening with whatever. But I wouldn't trust the orange foam on any critical application.

If it's multifamily, where a fire could spread to several floors and across many units, I expect to see clean openings and fire caulk and some kind of intumescent seal at plastic penetrations.

Link to comment
Share on other sites

As long as it is not fire rated construction and that chase is less than 4 stories, you can use the list of materials in the IRC R302.11, or approved materials, which is essentially the list Bill provided. Now, let's say you want to use a material not on that list such as sheetmetal or foam. Go to your AHJ and get it approved. The main thing is, it must provide an effective fire barrier between separations. If you are not dealing with rated fire walls or shafts, then this std. applies.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...