Although this is NM country, I don't think I have ever seen a gas furnace installed with anything other than hardwired armored cable for the 120-volt supply. No one, even in the worst of homes. An appliance cord set to a receptacle might be kosher(?), but I'm pretty sure I have never come across that. Kurt's exposed NM must be a Harry Homeowner install.

Link to comment
Share on other sites

It's funny how different things are from one part of the country to another. I did a seminar this last weekend in Reno and the inspectors there told me that they see nothing but cord-and-plug connections, despite the fact that the code prohibits it, and that UL has never listed a forced-air furnace with a cord-and-plug connection. Around here we see a few jack-leg installations with NM cable. Kurt's is relatively clean. Aside from the potential damage issue that Marc mentioned, usually the problem with NM is that it is not secured properly and that it is strung through the air, rather than following the building surfaces and framing.

Kurt, it isn't NMC - it is just NM. NMC is a special type of cable used in barns and rated for corrosive environments. Look on pages 246-252 for more than you ever wanted to know about NM, and on page 251 for the skinny on NMC.

Link to comment
Share on other sites

That installation is so ubiquitous in our area it's become one of the things that makes every report like neutrals and grounds under the same screw and NMC issues under sinks. I don't think I've ever seen a furnace with compliant wiring.

..........what Chad said. I can't remember when I've seen a furnace wired with anything other than NM.........Greg

Link to comment
Share on other sites

Since exposure to physical damage is not clearly defined, it seems that in some parts of the world inspectors are touchier about it than in other parts. Jim, in Maryland don't you folks routinely see it on basement walls? Looking at this photo of some fans in a basement, would it draw a correction notice in your part of the world? Around here, it would be written up as a violation of 334.15(A) & (B).

Click to Enlarge
tn_2013423213346_334.15.jpg

49.93 KB

Link to comment
Share on other sites

Kurt, it isn't NMC - it is just NM. NMC is a special type of cable used in barns and rated for corrosive environments. Look on pages 246-252 for more than you ever wanted to know about NM, and on page 251 for the skinny on NMC.

Double thanx.

I'm learning whole big bunches of new stuff with the new book. It's really wonderful.

Link to comment
Share on other sites

Doug,

It was typical to see the NM on furring strips, although sometimes I did see it run just on the block.

Couple of issues in the pics, one not secured within 12" of the boxes and IMO it does not follow the building surface closely enough due to the lack of being unsecured.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...