multi wire circuit


John Dirks Jr

Recommended Posts

I suspect this one might not pose a problem but I wanted to run it by the gang to get opinions.

As you can see, two hots from a 14/3 are on the same breaker (same phase). The breaker is listed for two conductors so no issue with double tap. Since both hot conductors are fed by the same 15amp breaker, the shared neutral for this multi wire circuit should not ever be overloaded since the combined currents of both hots would trip the breaker at anything above 15amps. Thus, the neutral would not be subjected to an overload. Am I thinking this through correctly? The label on the panel listed both hots as serving the living room. The way I see it, that really no different than having a single hot serving the entire living room.

I can't see a problem with this arrangement. Can any of you?

Click to Enlarge
tn_20136112248_P1360953.jpg

56.79 KB

Link to comment
Share on other sites

What makes you think a neutral is shared?

If it were, you need to consider what gauge wire is required for a 30 amp circuit (10). This is the wire gauge required for that neutral. The currents are additive because they share the same bus bar (1/2 phase).

So the current in both circuits 'hot' wire could be just under trip threshold for the breaker (say 14 A each) then the total current in a shared neutral is 28 Amps.

Ultimately it depends on how many devices are on each 'leg' of that breaker circuit. Beyond the scope of a home inspection.

Link to comment
Share on other sites

What makes you think a neutral is shared?

If it were, you need to consider what gauge wire is required for a 30 amp circuit (10). This is the wire gauge required for that neutral. The currents are additive because they share the same bus bar (1/2 phase).

So the current in both circuits 'hot' wire could be just under trip threshold for the breaker (say 14 A each) then the total current in a shared neutral is 28 Amps.

The two hots are using a single neutral. I traced it and verified it.

Now, think of it like this. In order for there to be 28 amps coming back on the neutral, there would have to be 28 amps flowing through that breaker (both hots are on the same breaker). Tell me how 28 amps is going to flow through that 15 amp breaker. It won't. The breaker will trip before the neutral is overloaded. It caught me at first but after I thought about it, I cant see a problem.

Link to comment
Share on other sites

...The two hots are using a single neutral. I traced it and verified it...

In that case, the only issue I see is that the two breakers serving the MW circuit do not have a common handle.

Did you confirm that the two hots are on separate poles? They should be.

I'm not understanding Bob K, not that I need to.

Marc

Link to comment
Share on other sites

Mr. Dirks, this is not a multi-wire branch circuit. The two ungrounded (hots) have no voltage between them. While it's an odd connection, depending upon how the circuit is installed, there is nothing wrong with it and nothing unsafe; as far as the picture goes. Two wires from the same hot leg on a listed two wire termination circuit breaker is no different than connecting (wire-nutting) a wire in a splice/junction box. IMHO it is nothing you should call out. :-) Additionally, in a true multi-wire branch circuit (shared neutral) the neutral current will actually be lower than that of separate branch circuit neutrals and not the sum of the currents from each branch circuit. Therefore the neutral doesn't have to be larger than the branch circuit "hots".

Link to comment
Share on other sites

For the record, the report was delivered before I started this thread. I did not write it up. Initially, when I first removed the cover I thought it was an issue. But when I realized it was the same breaker, I backed off.

In any case, I would rather issue an addendum than a correction to a report. In this case, I didn't have too.

Link to comment
Share on other sites

It's not a multi-wire circuit, but I have little doubt that the installer intended for it to be one. It's also possible that it was one and got rearranged by an amateur.

If I were inspecting the house, I'd suggest having an electrician re-wire it to restore the multi-wire circuit.

Link to comment
Share on other sites

Goofy electrical issues (...and this is one of them) are the work of someone who didn't understand the systems they were working. Given the hidden nature of electrical systems, that means there are likely other issues you're not seeing. It's time for Sparky to pay a visit.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...