Panel #1, looks correct. If you measured for continuity with a DMM, there would be some resistance in the feeder from the main panel. A fraction of an ohm, maybe. That would be correct.

Panel #2 is simply wrong. There are bare ground conductors touching the panel box. So they are providing grounding that way, but bonding the neutrals to the sub as well, totally wrong.

Link to comment
Share on other sites

Correct, somewhat. What you have are equipment grounding conductors attached to a neutral bus in this sub. (Which is wrong in this case) Both of those bus bars on each side are neutral conductor connection points and are tied together with an insulated bar behind the panelboard. What is needed is a grounding bus bar that is connected (bolted) to the metal enclosure with the equipment grounds (including the feeder equipment ground) stabbed there. Additionally that grounding bus bonds the metal enclosure as well. Easy fix. Hope this helps.