Service Conduit


Mike Lamb

Recommended Posts

230.7 Conductors other than service conductors shall not be installed in the same service raceway or service cable.

Exception #1: Grounding conductors and bonding jumpers.

Exception #2: Load management control conductors having overcurrent protection.

Marc

Link to comment
Share on other sites

The bottom right 50 amp generic breaker QO knockoff. Acceptable or not?

If the breaker is "classified" for use in that panel (it'll have the word "classified" printed on it somewhere) then there's no question that it's ok.

Even if it's not, if the breaker fits in its position snugly without pushing anything else out of the way and if the cover fits properly over it, I don't say anything about it.

The only time I call out off-brand breakers is when they don't fit properly.

Link to comment
Share on other sites