230.7 Conductors other than service conductors shall not be installed in the same service raceway or service cable.

Exception #1: Grounding conductors and bonding jumpers.

Exception #2: Load management control conductors having overcurrent protection.

Marc

Link to post
Share on other sites

Ooooh. Are those coax cables?

Thanks, Marc.

I don't think they are coax but I didn't look closely. My attention was overwhelmed by a couple of wildly overcrowded conduits and what looked like over heated wires.

Click to Enlarge
tn_201311721028_183A.jpg

106.64 KB

Click to Enlarge
tn_20131172119_196A.jpg

67.16 KB

Link to post
Share on other sites

The interior surfaces of the enclosure do indeed look like arcing has taken place plus lots of wire nuts connecting red conductors to black ones.

Could it be that someone installed a new panel in the existing enclosure?

Marc

Link to post
Share on other sites

The bottom right 50 amp generic breaker QO knockoff. Acceptable or not?

If the breaker is "classified" for use in that panel (it'll have the word "classified" printed on it somewhere) then there's no question that it's ok.

Even if it's not, if the breaker fits in its position snugly without pushing anything else out of the way and if the cover fits properly over it, I don't say anything about it.

The only time I call out off-brand breakers is when they don't fit properly.

Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...