Main disconnect height


Tim Maxwell

Recommended Posts

Here is the code section from the 2011 NEC

240.24 Location in or on Premises.

(A) Accessibility. Overcurrent devices shall be readily accessible and shall be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 2.0 m (6 ft 7 in.) above the floor or working platform, unless one of the

following applies:

(1) For busways, as provided in 368.17©.

(2) For supplementary overcurrent protection, as described in 240.10.

(3) For overcurrent devices, as described in 225.40 and 230.92.

(4) For overcurrent devices adjacent to utilization equipment that they supply, access shall be permitted to be by portable means.

Link to comment