100 Amp main disconnect FRIED!


Erby

Recommended Posts

Any ideas what would cause this, other than a loose connection.

There was a 200 Amp Main panel and this 100 Amp Main Panel, both fed direct from the meter. The only thing the 100 amp panel served was the heat pump.

Click to Enlarge
tn_20144270304_B4U049.jpg

42.25 KB

Click to Enlarge
tn_201442703027_B4U050.jpg

66.21 KB

Link to comment
Share on other sites

Is that a neutral conductor or a GEC that is blown apart in the bottom right of the panel? If it is a neutral conductor from the heat pump would the higher resistance on the left line created a load imbalance that would have over loaded a down sized neutral? If it is a GEC, a voltage surge?

Link to comment
Share on other sites

  • 2 weeks later...

I see three service entrance conductors inside conduit coming into the rear of the box - no cable there.

At the bottom of the box, an SE cable runs to the heat pump. The heat pump requires no neutral, so the braid is being used as an equipment grounding conductor.

A jumper runs from the neutral terminal to the accessory grounding terminal bar. The only function of this accessory bar seems to be to accommodate the sideways J-shaped wire that goes to the bonding bushing.

I don't see any grounding electrode conductor, which I would have expected to see.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...