I inspected two Lennox furnaces in the same building. Both are the same age and model installed at the same time by the same guy. The far left burners did not fire on either one. Might someone intentionally do this and for what reason?

Coincidence?

Click to Enlarge
tn_201539163145_162%20furnace.jpg

38.17 KB

Link to comment
Share on other sites

I'd say he's got the end orifice/ opening capped off. Otherwise, the flame rod you see on the functional far left burner would probably be placed @ the inoperative burner further left. At least most of them are.

Typically, the heat exchanger opening is capped when not in use though....

They're taking a 80k btu furnace and turning it into a 60k btu unit.

That flame rod proves flame for the burner "circuit". It needs to be @ the furthest burner over from the ignitor so that if all burners don't ignite, the gas valve closes. Otherwise, there'd be a risk for delayed ignition, which can be quite fun.

I tried to come up with a more clear explanation, but keep getting side tracked.