Prohibition against outlets above the tub


Marc

Recommended Posts

2012 IRC E4002.11 Bathtub and shower space. A receptacle shall not be installed within or directly over a bathtub or shower stall.

Arguable depending on where you place the emphasis when reading the rule as to within a bathtub... or within a bathtub... ...stall.

I would call this out just like a pendant light hanging over a tub.

Maybe if the tub deck was not there and it was a free standing tub a few feet away, but there is no doubt that if a window was on that wall it would have to be tempered because it forms part of the enclosure of the tub.

Also, E4003.11 Bathtubs and shower areas. Cord-connected luminaries , chain-, cable-, or cord suspended-luminaries, lighting track, pendants, and ceiling -suspended (paddle) face shall not have any parts located within a zone... This zone is all encompassing and includes the area over the tub or shower...

Even if it is not covered in the specifics of the code, it is a DUMB place for a TV and I am going to tell them lest their survivors come asking me why I did not warn about this!

Link to comment
Share on other sites

. . . Even if it is not covered in the specifics of the code, it is a DUMB place for a TV and I am going to tell them lest their survivors come asking me why I did not warn about this!

I suggest adding Article 101 to the NEC. It would consist of a single section, titled, "Don't do stupid things."

Link to comment
Share on other sites

I know this does not answer the question, but... assuming the TV can unplug itself before falling in the water, then what the heck?

TV falls and dangles from its cord. Bather sits up to catch it and put it back in its place. . .

On another note, how long can you watch TV before you look like a prune?

This was established back in the '50s: Exactly 1-1/4 episodes of I Love Lucy.

Link to comment
Share on other sites

Or somebody plugs something else into the outlet. Something that has a longer cord and would easily reach the tub.

Plenty of problems with this set up.

I know this does not answer the question, but... assuming the TV can unplug itself before falling in the water, then what the heck?

TV falls and dangles from its cord. Bather sits up to catch it and put it back in its place. . .

On another note, how long can you watch TV before you look like a prune?

This was established back in the '50s: Exactly 1-1/4 episodes of I Love Lucy.

Link to comment
Share on other sites

2012 IRC E4002.11 Bathtub and shower space. A receptacle shall not be installed within or directly over a bathtub or shower stall.

Arguable depending on where you place the emphasis when reading the rule as to within a bathtub... or within a bathtub... ...stall.

I would call this out just like a pendant light hanging over a tub.

Maybe if the tub deck was not there and it was a free standing tub a few feet away, but there is no doubt that if a window was on that wall it would have to be tempered because it forms part of the enclosure of the tub.

Also, E4003.11 Bathtubs and shower areas. Cord-connected luminaries , chain-, cable-, or cord suspended-luminaries, lighting track, pendants, and ceiling -suspended (paddle) face shall not have any parts located within a zone... This zone is all encompassing and includes the area over the tub or shower...

Even if it is not covered in the specifics of the code, it is a DUMB place for a TV and I am going to tell them lest their survivors come asking me why I did not warn about this!

The pendant light is clearly prohibited. The airspace above the footprint is also included. The footprint of the tub is less defined as it leaves room for interpretation if it includes the surrounding deck.

It may be arguable that that's a wet location.

That might be hard to argue, especially if that is only a tub, which it looks like based on the wall and window finishes.

Or somebody plugs something else into the outlet. Something that has a longer cord and would easily reach the tub.

Plenty of problems with this set up.

The sames issues could happen with a receptacle installed in a code compliant location 1/16" outside the footprint.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...