Mike Lamb Posted February 17, 2016 Report Posted February 17, 2016 Is there coded verse that a sink trap and tailpiece should be plumb? Click to Enlarge 33.29 KB
Bill Kibbel Posted February 17, 2016 Report Posted February 17, 2016 I don't know the exact language, but there are requirements for "Trap Setting". It states something like: Traps should be set level to maintain their water seals.
Chad Fabry Posted February 17, 2016 Report Posted February 17, 2016 As usual, Bill is right ...1002.7 Trap setting and protection. Traps shall be set level with respect to the trap seal and, where necessary, shall be protected from freezing. and, 1002.4 Trap seals. Each fixture trap shall have a liquid seal of not less than 2 inches (51 mm) and not more than 4 inches (102 mm), or deeper for special designs relating to accessible fixtures.
Les Posted February 17, 2016 Report Posted February 17, 2016 Is that the same for beavers and muskrats?
Chad Fabry Posted February 17, 2016 Report Posted February 17, 2016 Is that the same for beavers and muskrats? I get it. Funny stuff.
ghentjr Posted February 17, 2016 Report Posted February 17, 2016 Is that the same for beavers and muskrats? I get it. Funny stuff. Not for the beavers and muskrats.