I realize that AFCI is now 'required' for 'kitchens'....    what kind of reaction do you folks have about this in regards to the fridge being AFCI-protected ? My question is in regards to nuisance-tripping (off) of a device protecting a fridge... are local AHJs chiming-in??? 

Share this post


Link to post
Share on other sites

In NY, AHJ's have zero latitude to overlook a requirement. You cannot indemnify negligence.

Anecdotally, I haven't seen any nuisance tripping issues with the most recent wave of AFCI's. 

  • Like 1

Share this post


Link to post
Share on other sites

I have heard of nuisance tripping with the older GFCIs but not the AFCIs. Does the receptacle for the kitchen refrigerator have to be just an AFCI, or the combo receptacle that is both GFCI and AFCI as that might make some difference. 

Share this post


Link to post
Share on other sites

That's interesting.  Refrigerators have thermostats that switch the compressor on and off, and relays at the compressor terminal box that switch the start capacitor in and out of circuit.  Switches generate arcs.  Maybe the AFCI circuitry is designed to ignore these refrigerator arcs but this arcing can change as these parts age.  I can see AFCI's tripping when the appliance becomes older yet still works and ruining a great deal of food.

Edited by Marc

Share this post


Link to post
Share on other sites

Post-2008 AFCIs seem to be doing fine. They seem to be able to differentiate between "good" arcs and "bad" arcs. I'll start worrying about fridges on AFCIs when we start seeing problems with fridges on AFCIs. 

 

Share this post


Link to post
Share on other sites

I have first hand experience with afcis nuisance tripping. Brand new house, broke ground 5/16. There are 8 duplex in the garage gfci protected at the first receptacle and afci protected at the breaker. The start cap on my table saw would trip the afci about once every 20 starts. My brand new circular saw never tripped it.

Same house the bedrooms are protected with afci receptacles. My circular saw tripped each of them every time.

Different house 1 year older, afci breakers tripped every time halogen lights were turned on, and with high frequency when running a Kirby vacuum.

 

 

Share this post


Link to post
Share on other sites

The circular saw and Kirby aren't too surprising. They have messy power. Might be interesting to change the brushes on your saw to see if it makes a difference. The halogen light circuit probably has a shared neutral or a neutral-to-ground connection somewhere. 

Share this post


Link to post
Share on other sites

The codes need an adjustment to accommodate high wattage HID lamps and consumer power tools that use  brush/commutator motors like Toms's.

HIDs ( high pressure sodium, mercury vapor, metal halide) and fluorescents all generate sparks.  It's just the big ones that trip AFCI's, as per Jim.

Tom, does that table saw have a capacitor on it?  Mine does, no brushes.  Turning the thing on and off does generate arcs though, big ones, because it's a sizable motor.

Share this post


Link to post
Share on other sites
16 hours ago, Tom Raymond said:

Plug in halogen work light. No shared neutrals.

If you have the opportunity and the time, it might be interesting to wire the Kirby and the work light directly to the AFCI breaker to eliminate other variables in the household wiring. 

Also, do you know the brand of AFCIs that were doing this? 

Share this post


Link to post
Share on other sites

Remodeled kitchen and electrician had to install new AFCI/GFCI Siemens circuit breakers to comply with code. Now my 8 yr old Samsung 24 cu ft refrigerator trips the c/b every 12 minutes to as long as 4 days. Tried space heater on circuit and no problem. Plugged refrigerator into other AFCI/GFCI and they also trip but not as often. Refrigerator works fine on dining room non-GFCI circuit. Have spoken to appliance repair and Samsung service people and all say waste of time to come out and check refrigerator. They all say refrigerators should not be on GFCI. Spoke to city elect inspector and he said, sorry but code is code. Seems to be a catch-22 here.

Edited by jacbec

Share this post


Link to post
Share on other sites
19 hours ago, jacbec said:

Remodeled kitchen and electrician had to install new AFCI/GFCI Siemens circuit breakers to comply with code. Now my 8 yr old Samsung 24 cu ft refrigerator trips the c/b every 12 minutes to as long as 4 days. Tried space heater on circuit and no problem. Plugged refrigerator into other AFCI/GFCI and they also trip but not as often. Refrigerator works fine on dining room non-GFCI circuit. Have spoken to appliance repair and Samsung service people and all say waste of time to come out and check refrigerator. They all say refrigerators should not be on GFCI. Spoke to city elect inspector and he said, sorry but code is code. Seems to be a catch-22 here.

All refrigerators have a start relay that generates sparks but I wold imagine that the AFCI circuitry would have been engineered to disregard such sparks.  There may be something else going on that causing the tripping.

Share this post


Link to post
Share on other sites
On 11/22/2018 at 9:33 AM, jacbec said:

Have spoken to appliance repair and Samsung service people and all say waste of time to come out and check refrigerator. They all say refrigerators should not be on GFCI. 

1

*They* are wrong with regard to GFCIs. Plain & simple.

The UL standard for refrigerators requires them to have current leakage at or below .05mA. Modern GFCIs will not trip below 4mA. If a fridge is tripping a GFCI, it’s leaking *at least* 8 times as much current as it should. Your appliance people simply have no room for argument here.

I’m a little less sanguine about AFCIs. They’re often squirrely devices and I don’t have a lot of confidence in their ability to weed out “normal” arcing.

My suggestion is a bit irregular, but might be helpful. Try swapping out the Siemens AFCI/GFCI for a Square D (Homeline) or an Eaton one and see what happens. Each of these three brands is a little bit different from the others and you might find a sweet spot with one of them.  If so, you might have to live with a non-brand-matching breaker in your panel, which is technically incorrect, but probably better than living without the GFCI/AFCI protection, which seems like your only other choice, short of a new fridge.

Share this post