Bill, thanks for the offer. I'll wait on it. Don't want you to go through extra work.

Thanks also for that link - I looked in prior threads and didn't find that one.

The Goodman manual on that old thread was helpful, but didn't address the pitch of the pipe.

I had one yesterday that turned down out of the basement ceiling for about 24" and then out the sidewall. That Goodman manual doesn't address the pitch of pipe specifically.

Link to comment
Share on other sites

Whenever I run across the actual installation manuals, if I have "alone time" I glance over them (while my client is reading and signing the contract)

There is significant variation between manufacturers and even models.

I prefer to avoid creating an impression in my client that I am responsible for knowing the installation specifics for every model of 90+

If I have seen a 'potential' problem and find a specific reference in an available installation manual, I'll use it, but I otherwise leave it to "the experts."

Size/length of the vent depends on model, angles, etc. Charts required.

Pitch: my understanding is they should always be pitched back 1/4" ft back to the furnace.

FWIW, the biggest mistake I see is that they discharge too low above grade: in the US, every manual I have seen says 12" above grade or the 'anticipated snow cover, 18" in Canada"

Link to comment
Share on other sites

See following Goodman Two-Stage Gas-Fired Warm Air Furnace PDF http://www.dnmech.com/lit/IO-243.pdf Page 12, 17, and 18.

Horizontal runs of vent/flue piping must be supported every three feet and must maintain a 1/4 inch per foot downward slope, back towards the furnace, to properly return condensate to the furnace’s drain system. Allowances should be made for minor expansion and contraction due to temperature variations. For this reason, particular care must be taken to secure piping when a long run is followed by a short offset of less than 40 inches.

Vent pipe terminates 12" min. above highest anticipated snow level.

Jeff Euriech

Peoria, Arizona

Link to comment
Share on other sites

  • 1 month later...

The other very missed aspect of the direct venting of 90% furnaces is the vent pipe size. Manufactures state different pipe sizes based on BTU input of unit and venting length, where say a 75,000btu/hr unit may use 2 inch and a 100,000 btu/hr unit will use 3 inch. The install manual and the respective venting chart is really the key, there is no rule of thumb here. ........hvacman

Link to comment
Share on other sites

  • 3 years later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...