If that's a subpanel, it shouldn't be. Doesn't look like a floating neutral.

Originally posted by Jim Katen

I see an MLO subpanel with what seems to be an EGC landing on the neutral terminal bar instead of the grounding terminal bar.

Inattentive electrician?

- Jim Katen, Oregon

Link to comment
Share on other sites

Originally posted by ozofprev

If that's a subpanel, it shouldn't be. Doesn't look like a floating neutral.

I can't see well enough to be sure whether there might be a bonding screw on one of those neutral bars, but all of the mounting hardware looks to be plastic (oh excuse me...resin). The jumper is defintely insulated.

Brian G.

Resin-ating With My Clients [:P]

Link to comment
Share on other sites

It is a sub panel.

I should of turn off the flash when I took the photo

The neural is floating.

yes the grounds ends run past the bar.

The EGC runs to the water lines just like the exterior panel does.

The interior panel has been replaced. Most of the house has a 2 wire system.

Link to comment
Share on other sites

So that tie bar at the top of the bars is not connecting the bars?

Originally posted by Phillip

It is a sub panel.

I should of turn off the flash when I took the photo

The neural is floating.

yes the grounds ends run past the bar.

The EGC runs to the water lines just like the exterior panel does.

The interior panel has been replaced. Most of the house has a 2 wire system.

Link to comment
Share on other sites

Hi,

No, it connects those two buses, which are themselves isolated from the panel by resin mounting blocks. The installation would have been fine if a 4-wire cable had been used and the equipment grounding conductor was connected to the mounting lug at the top of that equipment grounding bus that's almost concealed by the left bank and that heavy grounding conductor were eliminated.

That looks like a newer panel, which means that the electrician screwed up. It's not unusual to see that on old panels but on a newer one? Uh uh. The NEC does not recognize running a separate equipment grounding conductor outside the feeder or in a separate path to that sub-panel, so that heavy bare grounding conductor has to go.

It's gonna be costly to pull a new 4-wire feed to that panel.

ONE TEAM - ONE FIGHT!!!

Mike

Link to comment
Share on other sites

Correct.

There is no floating neutral. If the bars are tied - as they are - then a separate ground bus is needed. This should not be a subpanel. I think people mistakenly believe that an isolated panel equates to floating neutral. Big mistake.

And you are right Mike, it will require some $$$.

Originally posted by hausdok

Hi,

No, it connects those two buses, which are themselves isolated from the panel by resin mounting blocks. The installation would have been fine if a 4-wire cable had been used and the equipment grounding conductor was connected to the mounting lug at the top of that equipment grounding bus that's almost concealed by the left bank and that heavy grounding conductor were eliminated.

That looks like a newer panel, which means that the electrician screwed up. It's not unusual to see that on old panels but on a newer one? Uh uh. The NEC does not recognize running a separate equipment grounding conductor outside the feeder or in a separate path to that sub-panel, so that heavy bare grounding conductor has to go.

It's gonna be costly to pull a new 4-wire feed to that panel.

ONE TEAM - ONE FIGHT!!!

Mike

Link to comment
Share on other sites

Hi Bob,

I know very little about conduit because I hardly see it. If that cable were fed with a 3-wire feed through conduit I suppose you could use the conduit itself as the grounding conductor back to the main panel but it would be almost impossible, wouldn't it, to push a fishtape back through a conduit past 3 wires, in order to pull a 4th conductor - saying that's what you wanted to do instead of using the conduit itself as the grounding path?

ONE TEAM - ONE FIGHT!!!

Mike

Link to comment
Share on other sites

Originally posted by hausdok

Hi,

No, it connects those two buses, which are themselves isolated from the panel by resin mounting blocks. The installation would have been fine if a 4-wire cable had been used and the equipment grounding conductor was connected to the mounting lug at the top of that equipment grounding bus that's almost concealed by the left bank and that heavy grounding conductor were eliminated.

Look more carefully. That is a 4-wire feeder. The two hots go to the main lugs. The white neutral goes to the right neutral terminal. The bare grounding wire snakes along the bottom of the enclosure and connects to the grounding bar. It connects at the bottom of the bar.

As far as I can see, the only problem here is that the heavy wire that leads to the water pipe is connected to the neutral terminal bar instead of the grounding terminal bar.

That looks like a newer panel, which means that the electrician screwed up. It's not unusual to see that on old panels but on a newer one? . . .

For the record, it doesn't matter. The rules haven't changed. The neutral was supposed to be floated at least as far back as 1947.

- Jim Katen, Oregon

Link to comment
Share on other sites

Wow,

You have got good eyes Jim. I had to open that thing is PhotoShop, blow it up and tweak the contrast to see that aluminum conductor against that shiny galvanized background.

Sorry, I stand corrected.

Still, if you've got the 4th conductor, why would you even want that grounding conductor, which is connected to the water piping, when you've got the grounding conductor as your path?

ONE TEAM - ONE FIGHT!!!

Mike

Link to comment
Share on other sites

Originally posted by ozofprev

Good eyes, Katen. That is a four wire. But the tie bar still has to go, yes?

No. There's no reason for it to go. The tie bar just connects the two neutral conductors. The whole neutral shebang is insulated from the panel enclosure.

The grounding terminal bar is bonded to the enclosure and it handles the few EGCs that land in this panel.

- Jim in Oregon

Link to comment
Share on other sites

Originally posted by hausdok

. . . Still, if you've got the 4th conductor, why would you even want that grounding conductor, which is connected to the water piping, when you've got the grounding conductor as your path?

ONE TEAM - ONE FIGHT!!!

Mike

If the sub-panel's in the same building as the service panel, there's no need for the water-pipe-conductor but I don't see any particular problem with it either.

- Jim Katen, Oregon

Link to comment
Share on other sites

Hmmm,

Okay, maybe I'm just cornfoozed then. I based the above on what I'd read in Hansen's book. Guess I need to go back and re-read it again, and again, and again. Don't know why, but even after 11 years I still struggle with understanding electrical systems and grounding and bonding paths. It still confuses the hell out of me. Sigh.

OT - OF!!!

M.

Link to comment
Share on other sites

Originally posted by Jim Katen

If the sub-panel's in the same building as the service panel, there's no need for the water-pipe-conductor but I don't see any particular problem with it either.

I had a thread about this somewhere, where I was trying to figure out if the code allowed a separate grounding electrode on a sub panel in the same building as the service equipment (needed or not). It does, so long as it's bonded with the other grounding system.

If the sub panel is in a separate building the grounding electrode is required, whether it needs a 3 or 4 wire arrangement, and also must be bonded to the other grounding system.

Gary, are you missing the small equipment ground bar half-hidden by the left-hand row of breakers?

Brian G.

Bonded...James Bonded [:-paperba

Link to comment
Share on other sites

The panel is inside the home as the exterior panel is on. My main concern is the large copper wire on the neutral bar going to the water pipe.

Thanks for the input from everyone. It is the first time I have seen it this way. To me there is no need for the large copper wire.

Link to comment
Share on other sites

HI Mike jumping in a little late now that the TIJ electrical guru has figured it out.

My thinking actually was to pull a fourth wire and yes you maybe right about the difficulty of pulling it through depending on the gauge wire and diameter of conduit.Guess thats why they make the wire lube.Personaly I used to just yank it all out tying it to the old stuff , half the time. Because in the city the old covering would deteriorate soon as you touched it.

Link to comment
Share on other sites

Brian, Thank you!!!

I thought I was losing my mind (not a huge loss, but still). I knew Katen wasn't gonna flub, so I was really stumped on why that tie bar was not the elephant in the room. NOOOO I did not see that little ground bar. Thanks, it's all good now. This is a great bunch of HIs.

Originally posted by Brian G.

Originally posted by Jim Katen

If the sub-panel's in the same building as the service panel, there's no need for the water-pipe-conductor but I don't see any particular problem with it either.

I had a thread about this somewhere, where I was trying to figure out if the code allowed a separate grounding electrode on a sub panel in the same building as the service equipment (needed or not). It does, so long as it's bonded with the other grounding system.

If the sub panel is in a separate building the grounding electrode is required, whether it needs a 3 or 4 wire arrangement, and also must be bonded to the other grounding system.

Gary, are you missing the small equipment ground bar half-hidden by the left-hand row of breakers?

Brian G.

Bonded...James Bonded [:-paperba

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest