Well...without actually delving into my IRC...

No way you can add a step on top of those CMUs and maintain an even rise. The step down from the front door would be OK only if the landing was 3ft deep and it doesn't look like it. The plain concrete upper step is different enough (no lip) that it probably breaks the rules for uniformity. Handrail. Oh...and that's some ugly brickwork either side of the entrance...(buried weepholes?).

Link to comment
Share on other sites

Thanks Darren, I must have had the rule confused with "interior" doors and stairways/landing requirements.

Here's the full code language on the subject.

R311.4.3 Landings at doors.

There shall be a floor or landing on each side of each exterior door. The floor or landing at the exterior door shall not be more than 1.5 inches (38 mm) lower than the top of the threshold. The landing shall be permitted to have a slope not to exceed 0.25 unit vertical in 12 units horizontal (2-percent).

Exceptions:

1. Where a stairway of two or fewer risers is located on the exterior side of a door, other than the required exit door, a landing is not required for the exterior side of the door provided the door, other than an exterior storm or screen door does not swing over the stairway.

2. The exterior landing at an exterior doorway shall not be more than 7¾ inches (196 mm) below the top of the threshold, provided the door, other than an exterior storm or screen door does not swing over the landing.

3. The height of floors at exterior doors other than the exit door required by Section R311.4.1 shall not be more than 7¾ inches (186 mm) lower than the top of the threshold.

The width of each landing shall not be less than the door served. Every landing shall have a minimum dimension of 36 inches (914 mm) measured in the direction of travel.

Link to comment
Share on other sites

Originally posted by Jeff Remas

Rich Moore you are certainly on the ball. They had to jack hammer out the bottom block in order to pour the sidewalk to the correct elevation.

If I was the owner, I would have left the foundation and made them rebuild the whole thing further away from the house so the landing could be extended to create a safer entry door condition.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...