GFCI feeding multiple areas


galanm

Recommended Posts

I have a house that has a garage outlet "protected" by a GFCI outlet in an unfinished room in the basement. I thought the protected areas should have individual - separate protection. Am I wrong? Common sense aside, is this allowed. The tripped GFCI in the basement turned off the freezer in the garage (right after a storm, I believe) the freezer doesn't get alot of use, so a week later (again, I believe) when it was opened, we found many science experiments.

Link to comment
Share on other sites

It is ok for a GFI receptacle to protect other receptacles. Having said that, most people in the know believe it is a bad idea to have a freezer plugged into a receptacle that is on a GFI protected circuit.

Is there another receptacle in the garage that is not on a GFI circuit? If so, try and plug the freezer in there.

Link to comment
Share on other sites

If you have another receptacle in the garage that is not protected by a GFCI, you should have a GFCI installed on it. If your freezer is causing a GFCI to trip, your freezer has a ground fault. You should either have the freezer repaired or replace it, so that you don't get a nasty shock some day when you are a better path to ground than the equipment grounding conductor.

The garage is not required to be on a different circuit than the basement. Receptacles in unfinished basements and garages are required to be protected by GFCIs. More than one receptacle can be protected by one GFCI.

There used to be an exception to the GCFI requirements in garages for receptacles that were not readily accessible or that were dedicated to an appliance that was not easily movable (like a freezer), but those exceptions were removed in the 2008 NEC. There were similar exceptions for receptacles in basements, but as of the 2008 NEC the only one that remains is for a permanently installed burglar or fire alarm.

Link to comment
Share on other sites

You might try the plug in alarms made to alert you if the power goes off to the appliance or a temperature sensing alarm.

Also, don't park the freezer in front of the GFCI.

There is no requirment for GFCI reset to be in the same room. I have seen some municipalities require upstairs bathrooms device to be on the same level, but that is just a local amendment.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...