1/0 AL to 12NM splice


John Dirks Jr

Recommended Posts

The pictures show a splice in the main panel of 12NM to 1/0AL. The 1/0 AL then runs to a box on the air handler where it changes back to 12NM to feed power to the blower.

Sparky is coming out for other reasons so I'll put a note in there for him to check this too. Meanwhile, help educate me. Is there anything specific that I should say is wrong with this arrangement?

Click to Enlarge
tn_20094201939_HPIM4944.jpg

53.77 KB

Click to Enlarge
tn_20094202013_HPIM4943.jpg

55.87 KB

Link to comment
Share on other sites

The pictures show a splice in the main panel of 12NM to 1/0AL. The 1/0 AL then runs to a box on the air handler where it changes back to 12NM to feed power to the blower.

Sparky is coming out for other reasons so I'll put a note in there for him to check this too. Meanwhile, help educate me. Is there anything specific that I should say is wrong with this arrangement?

Well, for starters, the connection between the grounding wires is entirely inadequate.

I can't see through the tape at the other connections but it looks like they might have used split bolts. Those are OK to connect copper to aluminum, but I don't know of any split bolt that will accept both a #12 wire and a #1/0 wire. The size difference is just too great.

- Jim Katen, Oregon

Link to comment
Share on other sites

Jim will correct me if I am wrong, but you can't go from a smaller size wire to a larger size. You can go from big to little, but not vice versa.

He hasn't come back so you must be correct.

This place had two panels, each with its own SEC from the meter. I couldn't get the cover off the panel on the left since some brilliant shmuck framed the opening to block the panel cover screws.

Thanks for the help everyone.

Click to Enlarge
tn_200942234135_HPIM4935.jpg

35.17 KB

Link to comment
Share on other sites

I couldn't get the cover off the panel on the left since some brilliant shmuck framed the opening to block the panel cover screws.

I can't tell you how many times I've told people that I need full access to the panel to pull the cover off, only to find they made just enough room to open the door. I think people don't realize those dead fronts actually come off......

Link to comment
Share on other sites

Jim will correct me if I am wrong, but you can't go from a smaller size wire to a larger size. You can go from big to little, but not vice versa.

I can't find anything that would prohibit changing wire sizes in either direction as long as the wires are rated for the ampacity and the overcurrent protection is adequate for all the sizes. For a big jump in size, you'd have to make the connection in several steps.

- Jim Katen, Oregon

Link to comment
Share on other sites

I can't find anything that would prohibit changing wire sizes in either direction as long as the wires are rated for the ampacity and the overcurrent protection is adequate for all the sizes.

I swear I've read somewhere that for long runs of wire, you can run say a 15 amp circuit with 12 gauge wire stepped down to 14 gauge wire (for voltage loss), but not the other way around. Now I need to find out where I read that.

I guess I need to invest in a copy of the current NEC and study up on it.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...