GFCI receptacles can only protect what is downstream of the GFCI. The lines remain hot between the panel and the GFCI.

So, technically speaking, Yes it must be the first one if you want to protect each outlet on the circuit.

If you want to protect all of the circuit, including wiring, it should be a GFCI breaker in the panel.

Link to comment
Share on other sites

If you install a GFCI outlet to protect an entire branch line, does it have to be the first outlet on the line? Thanks.

It can't protect anything that's upstream of it.

If you want to protect the "entire branch line" then you'll have to install a GFCI breaker.

If you just want to protect every outlet in the circuit, you can install a GFCI receptacle at the first outlet.

- Jim Katen, Oregon

Link to comment
Share on other sites

  • 2 weeks later...

Say the GFCI is in a bathroom on the first of two outlets, but the light is downstream. Is that bad? Or just not preferred? Or both?

Thanks!

I'm not aware of any rule against it.

Some people think it's a bad idea because, when the GFCI trips, the light will go out and you could fall and be injured in the dark. I think that, if you can't find your way out of a dark bathroom, your problems aren't related to a GFCI.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...