Sanitary tees are not allowed to be used in a horizontal to horizontal drainage configuration (IPC table 706.3). I don't think it being on a pump discharge line would make any difference. I'm not sure the pressure 90 (or quarter bend, if you like) should be used either. I would have also preferred the check valve installed on the horizontal pipe as it will be holding quite a head of water in a vertical installation.