KGarten 0 Posted June 24, 2009 Report Share Posted June 24, 2009 Sanitary tees are not allowed to be used in a horizontal to horizontal drainage configuration (IPC table 706.3). I don't think it being on a pump discharge line would make any difference. I'm not sure the pressure 90 (or quarter bend, if you like) should be used either. I would have also preferred the check valve installed on the horizontal pipe as it will be holding quite a head of water in a vertical installation. Quote Link to post Share on other sites
Jim Katen 148 Posted June 24, 2009 Report Share Posted June 24, 2009 This 2â⬠Quote Link to post Share on other sites
Richard Moore 0 Posted June 25, 2009 Report Share Posted June 25, 2009 Jim, don't you mean a wye or a combo? I didn't think any "Tee's" were approved for vertical to horizontal. Quote Link to post Share on other sites
Jim Katen 148 Posted June 25, 2009 Report Share Posted June 25, 2009 Jim, don't you mean a wye or a combo? I didn't think any "Tee's" were approved for vertical to horizontal. Oops. Yes, I misspoke (typed). It should be a wye or a combo tee. Quote Link to post Share on other sites
Mark P 6 Posted June 25, 2009 Author Report Share Posted June 25, 2009 Thanks guys - checks are in the mail. [:-hspin] Quote Link to post Share on other sites
Les 80 Posted June 25, 2009 Report Share Posted June 25, 2009 Mark, Don't forget my check. I read this topic and agree with Jim and Richard. I no longer have a checking account so could you make it a money order? Quote Link to post Share on other sites