Meter 200CL, 225 amp service?


Paul MacLean

Recommended Posts

Originally posted by Paul MacLean

On a 1997 large house yesterday I found a meter marked 200CL and the service entrance panel was rated for 225 amps with a 225 amp main breaker.

Is this a problem? If so what would you say?

Thanks!

It depends on the size of the SEC. If it's rated for 225 amps (3-0 copper or 250kcmil aluminum), I'd say it's fine for a 225-amp service. If the SEC is too small, then I'd say that the main breaker's too big.

Remember that a class 200 electric meter is actually rated for a maximum load of 250 amps. The "200" designation is 80% of its maximum capacity, often called its "continuous rating" because it's rated to pass 80% of its full load "continuously."

It's the same thing with Class 320 meters. They're usually installed in 400-amp services.

- Jim Katen, Oregon

Link to comment
Share on other sites

Katen said "Remember that a class 200 electric meter is actually rated for a maximum load of 250 amps. The "200" designation is 80% of its maximum capacity, often called its "continuous rating" because it's rated to pass 80% of its full load "continuously."

That's exactly what I was looking for. The SEC and main breaker supported 225 amp service, but I didn't know about the meter ratings.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...