Code cite 4 painting plastic vent pipe above roof


David Meiland

Recommended Posts

The requirement in the Uniform Plumbing Code is not in the code itself but in Appendix I "Installation Standards". How far back it goes I don't know.

It's in both the 2000 and 2009 as those were the editions that CA adopted.

Installation Standard For

ABS BUILDING DRAIN, WASTE, AND VENT PIPE AND FITTINGS

IAPMO IS 5-2003

2.2.3 Exposed Piping

Piping shall not be exposed to direct

sunlight. Exception: Vent piping through

roof. Plumbing vents through roof, exposed

to sunlight, shall be protected by water base

synthetic latex paints. Adequate support

shall be provided where ABS piping is

exposed to wind, snow, and ice loading.

Installation Standard For

PVC BUILDING DRAIN, WASTE AND VENT PIPE AND FITTINGS

IAPMO IS 9-2003

2.3.3 Exposed Piping

Piping shall not be exposed to direct

sunlight. Exception: Vent piping through

roof. Plumbing vents through roof, exposed

to sunlight, shall be protected by water base

synthetic latex paints.

Adequate support shall be provided where

PVC piping is exposed to wind, snow and

ice loading

As a side note in the "Dwelling Requirements of the Uniform Plumbing Code, 1997" they don't list Appendix I.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...